M

MJS9691

We have a new ceramic hob (6kW) factory prewired in 2.5mm flex and oven (2.6kW) prewired in 1.5mm. After diversity calcs the existing supply 32A protected 6mm (9m run) suggest a more than adequate supply for both appliances however:-

Some electricians are suggesting further protection of the flex beyond the outlet plate to protect the individual cabling on the appliances with FCUs and some say its OK to wire directly into a dual outlet plate with no further protection. Some Electricians are even suggesting removing the factory fitted cables and replacing with 6mm right up to the appliance.

Is there any definitive rules on this, or is this purely down to the electricians choice i.e. is it necessary or not to protect the 1.5mm flex cabling in the event of a fault on the appliance and it somehow drawing more current than the cable can take. There is no information on appliance fusing or protection in the installation manuals of either appliance.

Views on this matter would be appreciated as it still appears to be a grey area reading through the posts with installations not standardised...

Many thanks
 
So what happens if subjected to a fault current less than 160A? i.e if Zs ≥1.44?

e.g: If we have a Zs of 1.5

K =115
S =1.5
I = 153

therefore (115² x 1.5²) / 153² = 1.27s

So at a fault current of 150A the 1.5mm flex will reach max temperature in 1.27s, but according Fig 3A4 the 32A MCB will act in around 15s?

Then in this scenario, with an MCB as opposed to a fuse, and a 1.5mm cable, you have a problem. Zs being exceeded however doesn't neccesarily mean that the cable's maximum operating temperature will be exceeded too under fault conditions.
 
Then in this scenario, with an MCB as opposed to a fuse, and a 1.5mm cable, you have a problem. Zs being exceeded however doesn't neccesarily mean that the cable's maximum operating temperature will be exceeded too under fault conditions.

I'd go as far as saying, ''UNLIKELY'!!

Another reason why you should never be happy with only achieving the max Zs values when designing circuits/installations!! Then again we DO have our cure all /get out of jail card RCD devices!! lol!!
 
I'd go as far as saying, ''UNLIKELY'!!Another reason why you should never be happy with only achieving the max Zs values when designing circuits/installations!! Then again we DO have our cure all /get out of jail card RCD devices!! lol!!
Ah yes, those magical devices that cure all problems! Haha
 
I'd go as far as saying, ''UNLIKELY'!!

Another reason why you should never be happy with only achieving the max Zs values when designing circuits/installations!! Then again we DO have our cure all /get out of jail card RCD devices!! lol!!

With most TT's I guess you're relying on the rcd for fault protection though? I'm not talking about good or bad practice, just the fact that most will have Ra's too high to aid in disconnection solely from the MCB or fuse.

Before the advent of RCD's I'm assuming far more care was taken with regards supplementary bonding and cable selection?
 
Thanks for the replies everyone I see that "greyness" was thrashed out in the end;

So to conclude, we're good to go into the dual plate but will install a fire extinguisher next to the oven just in case?:rofl:
 
With most TT's I guess you're relying on the rcd for fault protection though? I'm not talking about good or bad practice, just the fact that most will have Ra's too high to aid in disconnection solely from the MCB or fuse.

Before the advent of RCD's I'm assuming far more care was taken with regards supplementary bonding and cable selection?

I can take you to more than just a few Domestic TT systems in the Essex area, that have Ra values better than some local DNO TN-S Ze values and no the gardens aren't full of copper rods either. lol!

One thing about the older TT systems, the electricians of the time understood the how's, why's and where's, of TT'ing and they didn't use thin twigs bashed in the ground right next to a wall!! ...lol!!
 
All im going to say on the matter is you are finding 8.5 kw hobs wired in non tri rated 2.5mm flex protected by 32 amp mcb's way over loaded if all the hobs are on in my eyes its wrong should be a minimum of 4mm but who am i ill wire it up if it goes wrong it was installed in accordance to the manufacturers instructions there problem not mine
 

Reply to Oven Hob Flex protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
357
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
736
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
519

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top