The house's existing double oven was wired by plug connecting into the 2.5mm kitchen ring final.Would be interested to hear the reason behind the question. One might suspect an issue has arisen right or wrong (?)
With regards Isolation a point to consider, it is not unheard of for appliance delivery teams to refuse to connect a new oven if no local Oven / Hob Isolation in the form of the switch is present.
Devil's advocate mode: The CU main switch would provide DP isolation.I guess one answer to your question could lie in the oven manufacturers installation instructions - if they say to use a 2 pole isolation switch, then the suggestion of using the MCB wouldn't comply (assuming that's a single pole disconnect).
I started under the 14th edition which became 15th mid apprenticeship. The 14th Edition of the IET wiring regulations did have a distance of 6 ft maximum distance stipulation for a cooker switch (becoming 2 mtrs in Amendment) . This was done away with [I believe] in the 15th Edition. Such a requirement is not now the case.Devil's advocate mode: The CU main switch would provide DP isolation.
Isn't distance a factor? Isolator should be within 2m of what it isolates
Regulation 132.15.201, while not applying specifically to cookers, requires “Effective means [of isolation], suitably placed for ready operation… so that all voltage may be cut off from… all equipment, as may be necessary to prevent or remove danger”.Hi,
For a double oven hard wired on its own dedicated oven circuit, is a separate isolation switch still required, or is the circuit breaker at the consumer unit (located nearby in the kitchen cupboard) adequate to isolate the oven?
Much appreciated!
It has already been mentioned on the need to refer to manufacturers instructions.The house's existing double oven was wired by plug connecting into the 2.5mm kitchen ring final.
Reply to the thread, titled "Oven Isolation" which is posted in DIY Electrical Advice on Electricians Forums.