haj

-
Arms
Joined
Nov 6, 2008
Messages
256
Reaction score
45
Location
East Yorkshire
Customer wants to plug his new oven into the kitchen ring i said that it still needed to be on its own supply even though its on a plug. What do you all thinl ?
Cheers :)
 
I suspect on that rating the oven is a built in single oven (no hob) if so it can be plugged into the ring but for isolation purposes then a 20A d,p, switch above the worktop can control it.

If you feel doubtful & want the customer to agree to add another circuit try the following tact; "the problem with kitchens is the loading is always the highest in the house & adding another 2.3 kw, all be-it intermittently, increases the risk of onerloading the circuit" (especially if washing machine, tumble drier & dishwasher are installed)
 
The cooker usually is on its own circuit with a cooker outlet plate and separate isolation switch for emergency's this circuit can be down rated to 16amp at the DB and a socket fitted but I would not plug the cooker into a rink main I would advise your customer it may well lead to overloading of the circuit have you worked out the total loading of the ringmain and checked that the socket is not a spur from a spur.
some small belling counter top cookers are designed to plug in to a ring it isnt one of those is it,if so check the manufactures info it could be ok.
 
Any cooking appliance rated at 2kW and above should have its own dedicated radial from the CU to prevent the RFC from being loaded for long periods.

However, if a new radial is not possible then it may be plugged into the ring, but i would say, only if its a dedicated kitchen RFC.
 
Any cooking appliance rated at 2kW and above should have its own dedicated radial from the CU to prevent the RFC from being loaded for long periods.

However, if a new radial is not possible then it may be plugged into the ring, but i would say, only if its a dedicated kitchen RFC.

Hi Jason i have pulled the cooker circuit back from the otherside of the kitchen and put a ccu on ready then the cooker comes with a plug on so customer thinks just bang it in a socket:eek: i say no it still needs to be on its own supply to prevent overloading the ring. Sounds as if i made the right call.
Thanks :):)

Thaks eveyone for all your views.
Regards Haj
 
Last edited:
Out of interest .... no dissent ... but (and there's always a but :)) .....

If an appliance comes with a lead ending in a moulded plug, I just make the assumption that it van only be 13 amps rating simply because it's a 13 amp plug .....

So, even if it's a cooker, with a plug on the end it doesn't need a dedicated circuit. Am I wrong?
 
Out of interest .... no dissent ... but (and there's always a but :)) .....

If an appliance comes with a lead ending in a moulded plug, I just make the assumption that it van only be 13 amps rating simply because it's a 13 amp plug .....

So, even if it's a cooker, with a plug on the end it doesn't need a dedicated circuit. Am I wrong?

Read my previous post, carefully. :)
 
I thought the building regs called for a dedicated cooker supply irrespective of if the oven's gas or electric. This will allow for "eventualities" such as the next person buying the house installing a massive range oven! :eek:
The electrical regs also state that good practice is a major part of compliance and I'd say installing a cooker circuit was good practice! ;)
 

Reply to oven on a plug top in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The motor is a common AC 120v 60hz motor. I've seen a hundred of them around for various things. It is attached to a single vent squirrel cage...
Replies
2
Views
231
It is possible that the particular socket you normally use in the kitchen is worn, or there's a wiring issue behind, contributing to the heating...
2
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top