I am often installing two 3.5kw ovens in one kitchen which amounts to 30amps.
I cant see that there are any problems with supplying them both with a single 4mm on 32mcb, (installation method c)
i have normally supplied it in 6mm but just wondering really. is it just bad practice, in case they uprate the ovens?