I am often installing two 3.5kw ovens in one kitchen which amounts to 30amps.
I cant see that there are any problems with supplying them both with a single 4mm on 32mcb, (installation method c)
i have normally supplied it in 6mm but just wondering really. is it just bad practice, in case they uprate the ovens?
 
I am often installing two 3.5kw ovens in one kitchen which amounts to 30amps.
I cant see that there are any problems with supplying them both with a single 4mm on 32mcb, (installation method c)
i have normally supplied it in 6mm but just wondering really. is it just bad practice, in case they uprate the ovens?
Will depend on what the cable sizing calculations turn up, doesn't it???????????
 
So bizarre when you run a 6mm then from the cooker outlet plate you use their cable that is a 1.5 or 2.5mm flex - I sometimes shake my fist at technological improvements!
I’m deffo one for 4mm runs if cable length and load don’t scupper the idea.
More people are having duel fuel so it’s a piddly oven that will never get over 9 amps with the wind behind it!
 
Good thread, I've had this discussion before. Simply put do the calcs on the cable / installation method and fit the right cable - if that's 4mm then so be it. However, a look at the manufacturers data sheet will advise the size they recommend (this has little regard to the installation method of course)! I do wonder how many ovens were fitted (with installation calcs) and then loft / void was filled with insulation maybe years later negating the installation!
 
Remember - if the oven is delivered and fitted by the supplier, they will simply not install it if they deem the cable the wrong size and they are told the 'minimum' size it should be. Your calcs may be correct but the oven / hob doesn't get fitted and you get called back - not good.
 
I think that, in this instance, future proofing seems to be a smaller CSA cable - I’m kidding but does seem to be the case!
 

Reply to oven supplies 4mm or 6mm??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yes, for example: https://kingsmillindustries.com/product/km2-20-10-sc/ However, the reality is the L-N-E style are far more useful in general as...
Replies
2
Views
979
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top