Hi I have recently come accross a couple of instances where the feed to the house is via Overhead cable, but is labled up at the service head as PME. In these instances should the supply be treated as a standard TNCS system - even though the supply is fed from overhead?:rolleyes:
 
Thats Ze isn't it Scot ? external. Or have i got the two mixed up. What would happen if you couldn't get that reading ?
I came across one of these,where the DNO had replaced all the cabling to a workshop in a back garden.The bloke had his fuse board replaced previous and it was connected up as PME,but the ZE reading was way over 0.35.In the end i just spiked it where the original one was before
 
yes Ze good that some people are paying attention besiders on my qwerty keyboard the letters are very close.

If it is a TN-C-S system and your ZE was above .35 ohms contact the supply authority and tell them. Its there earth they have to maintain it.
 
Last edited:
Seem to remember a problem with pme supplies that are underground and then rise up a pole and then travel a distance to
the point of use.
I think it was concerning true earth potential (the ground external) and the earth potential of the pme supply
because it also doubles as a neutral and therefore possible neutral currents,therefore any lets outside metal object
say a water pipe bonded to the building could have a potential voltage across it to the external ground.
Heard about this a while back,think further guidance is needed when dealing with such supplies?
 
They arent going to visit each property, but when a meter relocation is required, which involves the underground cable, instead of converting from TNS (if it is) to PME, it will stay as TNS.

Sorry, didnt make it very clear:rolleyes:
 
That will be interesting Jason what about the old 2 cores to houses they going round them all to sort them?
Still got an old 2 core in my house.They would have to dig up half the ground floor to replace it

Well, as an update to PME supplies, i have heard that SSE are now looking to do away with PME entirely and convert existing supplies to TN-S.

Not sure when and how tho.
Sorry mate,don't want to sound picky,maybe i'm wrong,but didn't you post something a few months ago that all TT systems were being upgraded to PME/TNCS by the DNO.All to be completed by 2013.:confused:
 
Last edited by a moderator:
Sorry mate,don't want to sound picky,maybe i'm wrong,but didn't you post something a few months ago that all TT systems were being upgraded to PME/TNCS by the DNO.All to be completed by 2013.:confused:

Yep, indeed i did and i was just as surprised when i was told.

Dont know what to believe anymore.

Trouble is, DNO's have their own rules and can change them whenever they see fit, especially if it suits them better.

I think TT systems still have to be changed, but im not entirely sure what to.
 
I have just had an internal meter moved outside fed from overhead cable, no signage to state PME infact earthing via rod. New meter now installed and labeled as PME same cable used. If i came across this again how can i verify earthing arrangement.
 

Reply to Overhead PME in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
818

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top