i have just moved into a 4 bed house with a 100amp main isolator in the consumer unit, PME supply with mcbs. The house has 2 showers of 8.5 kw each, electric oven 2.3kw, immersion heater (assumed to be 3.0kw), 3 lighting circuits, plus 3 ring mains for 13 amp sockets. Even after allowing for diversity is not the main isolator switch overloaded? It is quite possible that the oven and both showers could all be on at the same time (i.e. 84 amps), if the immersion was on as well this would be 97 amps, leaving only 3 amps for other things like kettle, tvs(x3), freezers(x2), lights, etc. One side of board has RCD , but no RCD protection to the showers (!), only to the 3 ring mains. Opinions and advice please.
 
The oven and immersion will have thermostats so will cycle on and off. The showers will only be on for relatively short periods of time so I think you'll be alright. If you're worried, perhaps you could set the immersion to come on at times the showers are not likely to be used?

I would definitely get the lack of RCD protection on the showers sorted out though!
 
As mentioned, the lack of RCDs for the showers is a priority.

The service fuse on the incoming supply will be a maximum of 100A, and it might well have a lower value fitted, e.g. 80A. It will withstand a significant overload for the time it takes some to have a shower (well, perhaps my daughter excepted).
 
Why not clamp (or get somebody to clamp) your meter live tail so that you can see what the actual demand is when you turn everything on. It is usually significantly less than you expect.

You can also get energy monitors quite cheaply which display your energy usage in real time, I came accross an 'owl' one Friday.
 
Quite the informative video on max demand / possible overload


Some interesting opinions that chap has ...... about 15 mins in a reference to non compliance of 314 for more than 1 cable in an mcb ........ hope he didn’t C2 that

On a reality level there are so many installs like this around ....... be interesting to see what happened next !
 

Reply to Overloaded consumer unit ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
775
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
949
  • Question
Not sure what you are saying in the section quoted so will ask you the question: Does a consumer unit have a main switch?
Replies
3
Views
329

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top