A question reguarding P.E.F.C and P.S.C.C using a megger 1553

Now i know this is a live test so lets say ive safely isolated ive got my megger im using the 2 wire lead option green and red.

So the board has RCD protection so i set my megger to the NO TRIP PFC ? CORRECT ?

Then test between LINE + EARTH for the P.E.F.C
Then test between LINE + NEUTRAL for the P.S.C.C

Then record the highest of the two results which = the PFC worst case scenario ? correct this is on a TNCS system by the way.

help would be appreciated many thanks volt
 
Hi all

A question reguarding P.E.F.C and P.S.C.C using a megger 1553

Now i know this is a live test so lets say ive safely isolated ive got my megger im using the 2 wire lead option green and red.

So the board has RCD protection so i set my megger to the NO TRIP PFC ? CORRECT ?

Then test between LINE + EARTH for the P.E.F.C
Then test between LINE + NEUTRAL for the P.S.C.C

Then record the highest of the two results which = the PFC worst case scenario ? correct this is on a TNCS system by the way.

help would be appreciated many thanks volt

Sounds spot on but if you can test on the supply side of the RCD without using 'no trip' (assuming it's within the DB) then your PFC reading will be more accurate.

The black lead on the 1553 will stay connected to the neutral bar throughout the 2 tests.

Your PEFC and PSSC should be almost identical on a TN-C-S system.
 
Sounds spot on but if you can test on the supply side of the RCD without using 'no trip' (assuming it's within the DB) then your PFC reading will be more accurate.

The black lead on the 1553 will stay connected to the neutral bar throughout the 2 tests.

Your PEFC and PSSC should be almost identical on a TN-C-S system.

Im a bit confussed now :) ahh forgive me i just noticed on the megger the top hole has the NO TRIP LOOP so this would be the neutral which would be connected thoughout the test ? correct ?

So the test would be a 3 lead test in reality then ? not a 2 as i thought ? is this correct ? many thanks volt
 
Im a bit confussed now :) ahh forgive me i just noticed on the megger the top hole has the NO TRIP LOOP so this would be the neutral which would be connected thoughout the test ? correct ?

So the test would be a 3 lead test in reality then ? not a 2 as i thought ? is this correct ? many thanks volt

I wasn't too clear there, if you can perform the test without using 'no trip' then it's a 2-lead test.

Using 'no trip' it's a 3-lead test.
 
I tend to use the Hi setting on the megger (- 4th along on the green area of the dial, if you know what I mean.) 2 lead test for PFC to earth and neutral
 
I tend to use the Hi setting on the megger (- 4th along on the green area of the dial, if you know what I mean.) 2 lead test for PFC to earth and neutral

yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?

So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?
 
yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?

So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?

Yes, no need for the 3rd lead on the full test.
 
yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?

So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?
that's how it is on the 1552. don't use no trip.
 
Reading through the megger leaflet quick start guide reguarding this PFC TEST

non tripping loop test [NO TRIP]

Select when testing ciruits with RCD protection fitted it says

High current loop test [HI]

for use on circuits with no RCD protection fitted

No trip PFC measurement [NO TRIP PFC]
phase to earth PFC
 
yes, but you only use no trip when measuring after the RCD, not before it

Thanks i get it now :)

So the test i would use on my TNCS system and the consumer unit being a MK dual RCD board would be

To set the megger onto the HI loop setting into the green area
then test form LIVE TO EARTH then LIVE TO NEUTRAL and record the highest reading as my PFC ?
 

Reply to P.F.C using a megger 1553 advice plz in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

  • Question
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...
Replies
1
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top