hi guys, done a periodic inspection today, obv you reccomend 17th edtion items to them change of db etc etc, but they will never change it.

todays inspection was tt system, with no time delay rcd, the only thing they had was a 30 ma rcd as main switch which controlled all 16 ways.

so therefore if there is a fault one circuit they lose the complete board.

so the 30ma main switch dont comply to 16th as there is no time delay and not 100a.

and now the 30ma rcd main switch dont comply to 17th because there is no discrimination.

i still thought tt systems had to have time delay tho.

whats your views on the above guys how would u go about it??

cheers.
 
Hi, 100ma was to provide a decent disconnection time.
Time delayed was there to stop nuisance tripping.

Where you have a 30ma rcd, this covers both the intention of the 100ma,
and the requirements of the 17th.

This is a very good situation but for the inconvenience part.
to overcome the problem, be it money, or, time, why not suggest a
3hr none maintained emergency light ? just a thought.

In my eyes, you would only need to code the lack of dual circuits ( 4 )
 

Reply to periodic inspection. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
567
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top