guys here are the results of a periodic report and i want to know what you think of the codes given, i feel they are not correct. the house has 4 floors containing 10 studio flats. each flat has a consumer unit. on the page containing particulars of installation at the origin the guy gave earthing conductor as being 16mm sq copper and clicked continuity check ok. now look at first fault reported.
faults
1 Inadequate main earthing conductor. needs 16 mm2. code 1 given
2 no cpc on any lighting circuit code 1 given
3 finger access to consumer units code 1 given
4 inadequate sub mains to each room. exceeding max currant carrying cap. discon times not met. code 1
5 cables feeding water heaters in zone 1 in bathroom clipped direct and not allowed in zone 1. code 2
6 no mechanicalprotection for cables serving coin meters and other equipment. code 1
7 bathroom lights not suitable code 1
8 washing machine in bathroom zone 2 not rcd protected or fixed code 1
9 rcd not tripping in time code 1
10 no equipotential bonding to gas water code 1
11 not enough sockets in each room code 2
12 damaged sockets code 1
13 no live conductor identified at switches, no cpc sleeve or grommets. code 2
14 no rcd on bathroom water heaters.
the guy then quoted 18000 to rewire the whole house.
also the lighting circuits have no cpc, so i understand i can put plastic screws and use class two gear and rcd and lable at cu, but where do i stand with unearthed metal back boxes. thanks
faults
1 Inadequate main earthing conductor. needs 16 mm2. code 1 given
2 no cpc on any lighting circuit code 1 given
3 finger access to consumer units code 1 given
4 inadequate sub mains to each room. exceeding max currant carrying cap. discon times not met. code 1
5 cables feeding water heaters in zone 1 in bathroom clipped direct and not allowed in zone 1. code 2
6 no mechanicalprotection for cables serving coin meters and other equipment. code 1
7 bathroom lights not suitable code 1
8 washing machine in bathroom zone 2 not rcd protected or fixed code 1
9 rcd not tripping in time code 1
10 no equipotential bonding to gas water code 1
11 not enough sockets in each room code 2
12 damaged sockets code 1
13 no live conductor identified at switches, no cpc sleeve or grommets. code 2
14 no rcd on bathroom water heaters.
the guy then quoted 18000 to rewire the whole house.
also the lighting circuits have no cpc, so i understand i can put plastic screws and use class two gear and rcd and lable at cu, but where do i stand with unearthed metal back boxes. thanks