Hi,

I’ve been recently working on a living trailer for a friend, when they have the supplies connected (240VAC 16A) they have nuisance tripping on the RCD. I’ve traced through and found an outside waterproof socket to be at fault, short circuit between live and earth. Removed the socket and tested, fault was not on socket, short still within the wiring. So I traced the cable back to a small joint box about 3M away. When I disconnect the cable from the box, then test of both sides of the connection box, there is no short. But as soon as I wire the cable back up the short comes back. I’ve completely removed the connection box and used inline crimps (to eliminate the connection box for testing) still the short is there. But when all is disconnected, each cable is fault free. Only when everything is connected will the fault reappear?

Any ideas?
 
Could it be that moving the cable is causing/breaking a short elsewhere (e.g. hole without grommet, etc)?
[automerge]1597144464[/automerge]
Also are you testing with an insulation resistance sort of meter (i.e. a "Megger" or similar that uses 500V) or a multimeter?
 
Could it be that moving the cable is causing/breaking a short elsewhere (e.g. hole without grommet, etc)?
[automerge]1597144464[/automerge]
Also are you testing with an insulation resistance sort of meter (i.e. a "Megger" or similar that uses 500V) or a multimeter?
I thought it was the cable, but was testing it while moving it round and especially around the gland areas, no luck.
Was using a multimeter at first, then IR tested it, no problem on either end while disconnected >999
 
TBH I'd replace the cable, could well be insulation damage that only shows when in certain positions.
 
The fault may be from L in one leg of cable to CPC in the other, so each cable tests good by itself. As Static points out, the CPC in one leg may not be connected to the chassis. If the L on that leg is faulted to the chassis only, it won't show up on its own CPC but it will via the chassis to the CPC of the other leg. Test all to chassis and each other, not just each cable separately.
 

Reply to “Phantom” Short on radial circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top