Hi, thanks in advance to anyone who can help.
I have been asked to install a 22kw transwave phase converter. I have been told it needs a 120a single phase supply and it can run a 3 phase board supplying various 3 phase machines.
I phoned and asked what the size of cable would be needed for the outgoing 3 phase supply from the converter to the 3 phase board. All I was told was that the outgoing cable from the converter to the 3 phase board depended on the maximum load it would be supplying as there is no overloed protection in the converter.
However the converter comes with a 32a 5 pin commando socket attached.
As I haven't fitted one before I just wondered if anybody could give any advice?
I was told the machine would probably be ok on an 80a type c breaker for the supply and 25mm tails. I also asked if disconnection times would be met because I wasn't sure how converter would affect zs values. Again all I was told was that I was only responsible for single phase supply not the outgoing!
Can anyone explain in layman's terms how these converters generate 3 phase from single phase.
Thanks again.
 

Reply to Phase converter problems in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
And have a very merry Christmas and a great new year all
    • Friendly
    • Like
Replies
2
Views
102
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
730
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
1K

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
452
I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...
Replies
7
Views
433

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top