Someone posted a thread about showing pictures of boards the other day. Here is one I saw today. Brand new install by an electrician apparently with 20+ years experience
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Pictures of Board work in the UK Electrical Forum area at ElectriciansForums.net
These are both very neat but I would want you to fit Intumescent pads over the cutouts at the back to maintain the fireproof integrity of the ccus.
did your rechargeble light run flat?
I reckon you could be right there Teldid your rechargeble light run flat?
There is no requirement to be fireproof, or fire containing.
it's not my board mate if you look at the post above the pic.As far as I was aware like dave says
Correct me if im wrong...
Looking at Reg 421.1.201 I believe the intent is to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames, and this is as true of metal consumer units as it is of plastic ones.
There is no specific requirement in regulation 421.1.201 for fire-rated cable glands or intumescent sealant to be used.
Good workmanship must always be applied, in particular to limit all openings around cables to a minimum.
There is no specific requirement in regulation 421.1.201 for fire-rated cable glands or intumescent sealant to be used
Why no identification/sleeving on your SWA
As far as I was aware like dave says
Correct me if im wrong...
Looking at Reg 421.1.201 I believe the intent is to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames, and this is as true of metal consumer units as it is of plastic ones.
There is no specific requirement in regulation 421.1.201 for fire-rated cable glands or intumescent sealant to be used.
Good workmanship must always be applied, in particular to limit all openings around cables to a minimum.
There is no specific requirement in regulation 421.1.201 for fire-rated cable glands or intumescent sealant to be used
Why no identification/sleeving on your SWA
This is our take on it, and our NIC assessors....... To maintain the integrity of the CCU and comply with the regulation all holes in the ccu should have a suitable fireproof seal.
To say there is no "Specific requirement" for cable glands is in my opinion just splitting hairs and goes against the intention/spirit of the Regulation. Its not hard to imagine a fire in the CCU spreading up the cavity and nit picking about the exact wording of the reg might make you feel better but I would rather have a cheap pad stuck on the back and sleep better at night.
Can you please define what this 'spirit' of the regulations is?
No it's not hard to imagine a fire spreading that way, but it is far better to prevent the fire starting in the first place by making sound connections than to attempt to contain it with unproven and probably unsuitable methods.
How is an intumescent pad going to help?
Fire will spread along the PVC cable and straight through your intumescent pad.
The steel enclosure is not fireproof, it is non combustible, there is a significant difference.
What method do you use to ensure that the intumescent pad is properly secured so that it doesn't in fact just fall off if exposed to fire? If it is stuck by an adhesive alones then the adhesive will melt and the pad fall off.
Sure Dave no problem, i'll explain it if your struggling..... The spirit of the Reg is to prevent fires in domestic installations spreading from the CCU to the fabric of the building.
I agree its better to prevent a fire starting in the first place by making sound connections but unfortunately that has not been the case over the last few years hence the new Regulation.
Method? We stick an oversized self adhesive intumescent pad on the back of the CCU over the knock-out, cut an horizontal line across the middle. Pass the cables through the pad and fix the board to the wall, no chance of it falling off and it acts as a grommet too. It really is a small expense for a far superior job.
Bill