Have you used the adiabatic equation (if permissable) to determine the minimum cpc size that would comply?
 
Pme vs TT

Hello all first post so go easy. I am presently carrying out condition reports on a chain of pubs my company started doing them 5 years ago when I joined my firm last year I was made aware I would be doing most of testing. I was quite happy about this got me outta the filth same money but rewarding in my eyes. Anyway what's your take on this Pub has Pme but was lacking power for domestic/commercial kitchen. Well there's a caravan plot next door owned by pub where a nic company took a supply including staked earth and run a sub main to pub Pme origin. This to me is **** but hey a few stickers and I would be of with it. But to take 2 x10mm earth's from switch fuse in pub straight into Pme met block! And here is my problem it's been bugging me I graded this with c2 potential danger should it be a c1 immediate danger due to what is essentially a high risk situation waiting for a fault to occur and kill someone.
I appreciate any and all responses
 
I think that this is an inappropriate situation but as you have said it is "waiting for a fault to occur and kill someone" therefore it is a C2 as there is no immediate danger unless a fault occurs.
I am pretty sure that connecting an existing supply to the DNOs PME earthing is not legal might be interesting to put that in comments (but check legality first!)
 
Re: Pme vs TT

there's a caravan plot next door owned by pub where a nic company took a supply including staked earth and run a sub main to pub Pme origin. .... But to take 2 x10mm earth's from switch fuse in pub straight into Pme met block! And here is my problem it's been bugging me I graded this with c2 potential danger should it be a c1 immediate danger due to what is essentially a high risk situation waiting for a fault to occur and kill someone. I appreciate any and all responses

I don't think there is any danger here at all.

First make sure I understand the configuration: Switch fuse in Pub close to supply head with final earth consisting of 2x10mm cables. Sub main from pub to caravan with CU in caravan. Caravan CU earthed with local earth rod. I cannot make out if you imply the submain has an earth and if it is also connected to the earth in the caravan CU. I am assuming that the caravan is fixed and is being considered as an Mobile Home (or outbuilding) rather than a Caravan as described in Reg 721.

First the 2x10mm earths. My understanding is that it is permissable to use two thinner cores wired in parallel to form a cable so long as they are of equal length and will therefore share the load correctly. In this case 2x10 being 20mm total exceeds the requirement for a 16mm earth (assuming a 25mm supply).

Second the earthing of the caravan. There have been many discussions on this board re "exporting" the equpotential environment of the supply head, some beleiving that you should do this, some beleiving you should create a seperate equipotential environment by installing a TT system in the out building. I don't know if there is any recent edict on this, but look at it in these ways. If the earth of the sub main is connected in the caravan then the earth rod can be considered as an extranious item of mental connected to the caravan (even if only through its own cable) and must therefore be bonded with a minimum of 10mm. If the earth of the submain is not connected then it is a TT system, should be fitted with a 100mA RCD and earthed with a minimum of 2.5 or 4mm (according to mechanical protection). To me both approaches are valid and present no risk.... or have I misunderstood somthng?

A side issue would be the size and nature of the earth conductor in the sub main. If it is for example a 10mm T&E supply then the earth would be undersize to act as bonding, while a 10mm core of a SWA cable would be. Then again some supply companies will not accept the earth included in a SWA cable as a bonding cable and require a seperate bonding cable connected directly to the met, exactly as shown in the Regs. Note also though that if the caravan were considered to be within the scope of Reg 721 then the bonding of the caravan must be to the earth of the incomming supply.
 
Last edited:

Reply to PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
417
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Commonly known as double knock, some pirs have a latch on time delay for a few seconds, giving time for the 2nd one to activate .
Replies
3
Views
365
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top