T

tedglen2

Hello all.

I have goggled filling T&E with plaster and there are a lot of responses saying plaster will corrode the cable?

Is this just a myth? Will I be ok to just clip the cables then plaster over myself!
 
May I say I don't like cables being in the wall without "basic protection" yes there is a tick box on the schedule of items inspected on both an Electrical installation certificate and an electrical installation condition report to say that the " basic protection" has been met.

I think you may have been ticking that box without understanding BS7671's definition of basic protection!
 
BS7671 Definitions.

Basic protection= Protection against electric shock under fault-free conditions. So capping has nothing to do with this what so ever.

So basic protection is the cable insulation?

It doesn't even need to be double insulated, that means singles clipped to a wall, no capping and plastered is O.K.

.
 
Yes but it is for all insulation on the circuit form the cable insulation to enclosures to socket fronts etc. In laymans terms no live parts can be accessed anywhere on the circuit if there is no fault on it.
 
So basic protection is the cable insulation?

It doesn't even need to be double insulated, that means singles clipped to a wall, no capping and plastered is O.K.

.
capping is not considered as additional protection....its there purely to stop plasterers (rough gits) from cutting into our cables with their trowels...
 
Put capping in don't put capping in. All the pictures on google I have seen have been with capping/conduit. Don't wanna put it in... Then don't, I get a better sense of pride when it's there, separates the men from the boys
 
Put capping in don't put capping in. All the pictures on google I have seen have been with capping/conduit. Don't wanna put it in... Then don't, I get a better sense of pride when it's there, separates the men from the boys
well if the walls are to be dry-lined then PVC/metal channel isn`t really necessary is it....you look at the job in hand first to assess what needs doing....then go with that....its the same for most things isn`t it....
 
you can still get oval conduit of course......its just with costs being more at the forefront of peoples mind nowadays.......i mean look at the first thing out of their mouths...
`how much?`
 

Reply to Plastering directly over T&E in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
Thanks for your time and opinion.
Replies
11
Views
1K
  • Question
Thank you for the speedy response! Have seen them on top of plaster in steel conduit before but guess it's not a common desire to have wires...
Replies
2
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top