Hi all.
The important part is that the socket is not fitted on the skirting because you state the socket is on a plastic mount so it's not in contact with the softwood therefore is compliant. Years ago wood was actually used as an insulator and the regulations have been changed to clarify this in Part P. If the socket was mounted to the skirting without a plastic mount BUT the wood is hardwood like oak or mahogany then it could be compliant.
The inspector is wrong and you have grounds to have the report amended.
The important part is that the socket is not fitted on the skirting because you state the socket is on a plastic mount so it's not in contact with the softwood therefore is compliant. Years ago wood was actually used as an insulator and the regulations have been changed to clarify this in Part P. If the socket was mounted to the skirting without a plastic mount BUT the wood is hardwood like oak or mahogany then it could be compliant.