More experienced help needed please. Scenario is Mains intake and MET(PME) outside the building in cupboard with KMF's (80A fuse) feeding flats via 16mmT+E. 2 flats gas meters are in cupboard at mains with 10mm bonds. 1 flat has gas meter in flat with no 10mm bond. Also no 10mm bonds to water. All flats have local 6mm bonding to gas and water from flat DB.
To run 10mm bonds to water and 1 gas meter will be a nightmare as being listed etc also would have to be run outdoors because would need access through others flats . Also loads of electrical work has been done without this being picked up.
All I wanted to know is what code to give this on EICR (I will probably be doing work). NAPIT tech guy said code 2 or 3, but wouldn't commit to one. I have heard others say if no signs of overheating on 6mm then no code. I asked NAPIT guy if i could give code 3 and satisfatory report he then said code 2.
Please help. Thank you.
 
NIC/Elecsa changed their recommendations for upgrading gas & water bonds to 10mm recently, there was a thread here recently. Seems Napit suggesting the same?

Do the said pipes require bonding, are they extraneous? Sounds as if the main gas & water enter property in the mains cupboard, just a thought?

PS: what about the earthing conductor to each flat?
 
Last edited:
Its all very well these organisations changing their recommendations BUT they do ABSOLUTELY NOTHING to inform the public and leave us to delivery the "news" and some customers simply think we are ripping them off by recommending unnecessary work!
 
Its all very well these organisations changing their recommendations BUT they do ABSOLUTELY NOTHING to inform the public and leave us to delivery the "news" and some customers simply think we are ripping them off by recommending unnecessary work!
But in fairness Murdoch, they are only quoting BS7671.
 
Yes I gathered that. What is the process to check if it's extraneous. Is it if its less than 23k ohms? Also if you get a reading of less than 0.05 ohms can you presume bonding is on even though you can't see bonding conductor. Thank you
 
Yes I gathered that. What is the process to check if it's extraneous. Is it if its less than 23k ohms? Also if you get a reading of less than 0.05 ohms can you presume bonding is on even though you can't see bonding conductor. Thank you

No you cannot presume that bonding is there. You can only state that a low resistance connection to the MET exists.

What you can presume is something about the person carrying out the report if they are so unsure about how to test an extraneous part and how to code such a common observation on the report.
 
No you cannot presume that bonding is there. You can only state that a low resistance connection to the MET exists.

What you can presume is something about the person carrying out the report if they are so unsure about how to test an extraneous part and how to code such a common observation on the report.

Thank you for your helpful reply. Much appreciated..
 
No you cannot presume that bonding is there. You can only state that a low resistance connection to the MET exists.

What you can presume is something about the person carrying out the report if they are so unsure about how to test an extraneous part and how to code such a common observation on the report.

Im going to take the Mrs to bed know, not my regs. book....
 

Reply to PME Bonding help! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
322
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top