The easiest thing is to create a TT system at the house. Use the PME earth for the swa cable supply then at the house end gland it off in an all insulated enclosure to separate the PME earth from true earth. Fit rcbos to each circuit.
 
I think this comes from Reg 543.4.1
Well if it's in the regs, then it's in black and white....just seems maddnes having a good earth at the DNO cutout, then at the DB end ditching it and then put in earth rod. Again , the University has several of its own substations with massive section boards that feed other large buildings (so technically the substation is the DNO supply) so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.
 
Well if it's in the regs, then it's in black and white....just seems maddnes having a good earth at the DNO cutout, then at the DB end ditching it and then put in earth rod. Again , the University has several of its own substations with massive section boards that feed other large buildings (so technically the substation is the DNO supply) so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.
The armour of those cables may be adequate to support bonding.
 
thanks for comments guys , i need all phases as massive house with a lift and various kitchens with big appliances etc , but i guess the main switch being 300ma rcd then me using 30ma rcbo units is the way , there is a 6 inch duct howeve its not a straight route and they didnt pull in a draw wire just the cable (bless them )
 
The armour of those cables may be adequate to support bonding.
Ah so smaller SWA cables may not be suitable for that. Funnily the cables I've seen used in this way were much bigger that 35mm2, 50mm upwards if I remember correctly.
 
thanks for comments guys , i need all phases as massive house with a lift and various kitchens with big appliances etc , but i guess the main switch being 300ma rcd then me using 30ma rcbo units is the way , there is a 6 inch duct howeve its not a straight route and they didnt pull in a draw wire just the cable (bless them )
Well I suggest you get a pet rat and train it to run through drain pipes with string tied to it, put it through your duct, then tie a rope to the string, then use rope to pull in earth cable.....job done;)
 

Reply to PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top