It's proposed in the 18th edition that any new pme installation is to have a rod added by the electrician that has has a resistance of 30ohms or less. What are people's thoughts on this? My main concern is the amount of services that are going to get hit with everyone driving rods in.....also my lowest reading on a rod ever was 40 ohms which I thought was good.
What everyone needs to remember is that the rest of the world already requires an Earth electrode on a TN-C-S system and always has.
We've always been proud to be well ahead of the rest of the world regarding electrical safety.....maybe we're falling badly back into line. I wonder why? Could it be due to cutting back on the expense of installation by supply authorities...or coming in to line with the crap standard of work and materials used overall in the present electrical installation industry.
A whole lot of both, perhaps?
542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3, as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2. Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to Earth.
542.2.3 Where foundation earth electrodes are installed the materials and dimensions of the earth electrodes shall be selected to withstand corrosion and to have adequate mechanical strength.
Biggest problem I found with the draft, was that instead of just printing the changes, they printed the whole damn thing.