Just been to do a PIR in a house in Stoke.
When I got there I found the service head with a 100amp main fuse,16mm tails and a small 6 way board protected by a 100ma 80 amp elcb.
I realise the tails need upgrading to 25mm and therefore the main bonding which at present is 6mm will also need upgrading to 10mm.
There seems to be no earth to the consumer unit at all,so I assume the large Zs readings I am recording are due to it finding a path to earth via the pipes in the house!! and not the suppliers earth!!
If I am to put right this installation then do I need to fit an earth rod? im assuming so!!
and also is the board satisfactory or would I have to fit a board with a 30 ma main switch??
or 100ma main switch and then individual 30ma rcbo's to each individual circuit??
kind regards Graham.