D

drewandsons

Just been to do a PIR in a house in Stoke.
When I got there I found the service head with a 100amp main fuse,16mm tails and a small 6 way board protected by a 100ma 80 amp elcb.
I realise the tails need upgrading to 25mm and therefore the main bonding which at present is 6mm will also need upgrading to 10mm.
There seems to be no earth to the consumer unit at all,so I assume the large Zs readings I am recording are due to it finding a path to earth via the pipes in the house!! and not the suppliers earth!!

If I am to put right this installation then do I need to fit an earth rod? im assuming so!!
and also is the board satisfactory or would I have to fit a board with a 30 ma main switch??
or 100ma main switch and then individual 30ma rcbo's to each individual circuit??

kind regards Graham.
 
are you sure there isnt a rod somewhere already..?
agree with you that its probably earthing through the pipes at the moment.
But I would explore the other possibilities.

Perhaps there is a rod but the main earth bond to it from the CU is missing?
Could it be that its supposed to be TNS and its been tampered with.. hence the missing main earth..

Think i would like some input from the DNO as what they think the earthing arrangements are at the property..
Then put that to the client if extra costs involved.
Document their answer if its anything less than getting DNO out to sort the service head..?


If nothing else, perhaps check the houses next door, either side, see what the earthing arrangements are.

Of course you could just bang in a rod until the Ze is low enough... !!
Personaly i'd like to know the reasons why its the way it is.
Depends how much time you have.
 

Reply to pme or TT?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
697
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top