Hi all, I've been surveying 12 blocks of flats today with a view to doing full eicr's on the lateral mains and landlord lighting supplies. All the main services terminate at a Henly distribution board with no cut-out or main fuses. See pic, I've done very little on pme supplies and wonder if this is the norm? Appreciate your input. Bill
[ElectriciansForums.net] PME supply query (and bulk out the title)
 
to me billsays it pme system .but looking at the picture where are the fuse boards!

Hi Buzz, This is in an intake cupboard at the bottom of each block. Inside the grey Henly distribution board are fuses. Then a lateral main to each flat with another fuse/cutout beside each meter.
[ElectriciansForums.net] PME supply query (and bulk out the title) [ElectriciansForums.net] PME supply query (and bulk out the title)

(On the first photo in my original post ignore the meter thats just a builders supply thats been put in)
 
Is the cutout and mainfuse in the shaped compartment under the Henley dist board? You've the cover off of the flats supplies but the incomer goes to that shaped box.
 
Is the cutout and mainfuse in the shaped compartment under the Henley dist board? You've the cover off of the flats supplies but the incomer goes to that shaped box.

I had a look in there and it's just a spreader box. Didn't take a photo though.
The set up is the same for the whole estate, I've not come across it before.
 
Much as I love electric cupboards I haven't seen enough set ups to comment any more. There'll be plenty experience along in a moment, you'll have it sorted by pudding time. All the best
 
No fuse switches just fuses.
One fuse in the large grey Henly board then the laterals run in conduits to each flat, outside each flat there is a small meter cupboard with another cutout fuse.
come back billsays with pics of all the set up of the meters bits and bobs .
and not with brown camera .
 

Reply to PME supply query (and bulk out the title) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
988
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top