Pool wiring, wago connectors | Page 2 | on ElectriciansForums
Discuss Pool wiring, wago connectors in the UK Electrical Forum area at ElectriciansForums.net
R
ryan24
Hi all
If wiring a pool on a 32amp breaker using 6mm cable for heater and wiring the pump of the same circuit. What would be the best way to join 3 x 6mm cables together in the junction box? The reason is the armoured in connected to heater then coming of that to feed fused spur for pump. Looked at using wago connectors but the heater is wired using flex which won't work on 6mm wago connectors
Thanks in advance
So you want to common 3x 6mm² together, one of which is flex? Simplest is something like these screw-terminal commoning blocks:
| RS Pro Non-Fused Terminal Block, 5 Way/Pole, Screw Terminals, 6 mm² Panel Mount, PC, 450 V | - http://uk.rs-online.com/web/p/non-fused-terminal-blocks/8680774/
Unlike Wagos they will acccept 6mm flex although you'll want to ferrule the flex ends.
OTOH if there's room to pop-rivet an inch of top hat DIN rail in the JB it would be neater to use low profile 1-in 2-outs.
Reply to Pool wiring, wago connectors in the UK Electrical Forum area at ElectriciansForums.net
I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
yeah. i think so. Details here..... https://www.electriciansforums.net/threads/havent-seen-tel-for-a-month.210295/