Poor install EICR 12 year old hotel | Page 4 | on ElectriciansForums

Discuss Poor install EICR 12 year old hotel in the UK Electrical Forum area at ElectriciansForums.net

conrad

-
Joined
Jul 3, 2015
Messages
117
Reaction score
31
Location
North wales
Carrying out an eicr. Thoughts on these DBs installed in each room. Around 20 have been installed in this manner with no gland on the supply SWA and the top surface of the DB completely removed.
Note the plasterboard hole is small in this image compared to some.
What do you think other than replacing baring in mind the rcbos for this DB can be ÂŁ100 alone. Paxolin to slide in etc? Time. Shame for the customer who has had this poor installation.
[ElectriciansForums.net] Poor install EICR 12 year old hotel
[ElectriciansForums.net] Poor install EICR 12 year old hotel

I have noted as C2 for a number of different reasons. As follows if you wish to read.
522.8.5.
The SWA cable entering the DB has no gland fitted. C2
701.411.3.3
Circuits passing through and supplying accessories in loaction containing bath/shower not provided with RCD protection. C3
527.2.1
Large Hole not made good in plaster board above DB to prevent the spread of fire. C2
411.3.3
No RCD protection on socket outlets, commercial premesis. C2 (Fridge Socket)
522.6.202
No RCD protection for cables buried in the walls. C3
416.2.2
Top surface of Distribution Board has been removed. The integrity of the DB has not been maintained during installation. ip4x not maintained. C2.

[ElectriciansForums.net] Poor install EICR 12 year old hotel
 
Of course it matters which edition it was designed to.
If an installation complies with the edition it was designed to, then as per BS7671 it is not unsafe.
It can’t be unsafe, otherwise the IET would be guilty of promoting unsafe installations.
 
Of course it matters which edition it was designed to.
If an installation complies with the edition it was designed to, then as per BS7671 it is not unsafe.
It can’t be unsafe, otherwise the IET would be guilty of promoting unsafe installations.
A perfect example is the fixing of wiring systems against premature collapse.
Knowing what we know now and following the deaths of firefighters, we can’t now say that an installation which complied to the 16 th edition or the 17th pre amendment 3 are necessarily safe in regards to that particular regulation.
Whether it complied before is irrelevant as we are not inspecting the installation to the date it was designed and installed .
It’s safety must be in regard to the current edition of the wiring regulations full stop.
Obviously if any non compliance’s do not warrant a FI ,C1 or C2 code it can be regarded as satisfactory for continued use but have recommended safety improvements issued to the client.
 
Last edited:
A perfect example is the fixing of wiring systems against premature collapse.
Knowing what we know now and following the deaths of firefighters, we can’t now say that an installation which complied to the 16 th edition or the 17th pre amendment 3 are necessarily safe in regards to that particular regulation.
Whether it complied before is irrelevant as we are not inspecting the installation to the date it was designed and installed .
It’s safety must be in regard to the current edition of the wiring regulations full stop.
That’s not a new requirement though is it?
We’ve always been required to install wiring so that it doesn’t present a danger.
All that’s happened, is the IET have addressed poor practices and clarified what is required.
 
That’s not a new requirement though is it?
We’ve always been required to install wiring so that it doesn’t present a danger.
All that’s happened, is the IET have addressed poor practices and clarified what is required.
As far as I’m aware we never had to prevent the wiring throughout the installation collapsing prematurely in the event of a fire.
Cables inside trunking, plastic saddles etc all acceptable as they where In previous editions of the regulations.
No mention of escape routes as that came with the 17 th edition amendment 3.
 
Last edited:
The fact that you were unaware that we were required to prevent the premature collapse of wiring systems in the event of a fire, is exactly why the IET decided to clarify the matter.

Every edition and amendment is published 6 months before it comes into force. During those 6 months, we are allowed to design and construct to either edition or amendment.
After the new edition or amendment comes into force, we are still allowed to construct a design which was made before the the new edition or amendment came into force.
There is no time limit on how long after the new edition or amendment comes into force, that we can construct the design.

If anything in the previous edition or amendment were considered unsafe, we would not be allowed to install anything designed to that edition or amendment.
Allowing us to do so would be endorsing unsafe practices.
 
The fact that you were unaware that we were required to prevent the premature collapse of wiring systems in the event of a fire, is exactly why the IET decided to clarify the matter.

Every edition and amendment is published 6 months before it comes into force. During those 6 months, we are allowed to design and construct to either edition or amendment.
After the new edition or amendment comes into force, we are still allowed to construct a design which was made before the the new edition or amendment came into force.
There is no time limit on how long after the new edition or amendment comes into force, that we can construct the design.

If anything in the previous edition or amendment were considered unsafe, we would not be allowed to install anything designed to that edition or amendment.
Allowing us to do so would be endorsing unsafe practices.

Theyre counting on you being competent and taking into consideration consequences of installing to previous editions etc. Come on. You are digging.
 
The fact that you were unaware that we were required to prevent the premature collapse of wiring systems in the event of a fire, is exactly why the IET decided to clarify the matter.

Every edition and amendment is published 6 months before it comes into force. During those 6 months, we are allowed to design and construct to either edition or amendment.
After the new edition or amendment comes into force, we are still allowed to construct a design which was made before the the new edition or amendment came into force.
There is no time limit on how long after the new edition or amendment comes into force, that we can construct the design.

If anything in the previous edition or amendment were considered unsafe, we would not be allowed to install anything designed to that edition or amendment.
Allowing us to do so would be endorsing unsafe practices.
Don’t insult my intelligence please , “the fact I was unaware “
Clutching at straws.
If it was required at the time it would have been in the regulations.
Double pole fusing was once a requirement, how did that one go?
So you must be stating that you’ve always installed wiring systems against premature collapse?
Ever since you’ve been an electrician you’ve always installed metal fixings to hold the cable in place inside trunking?
 
I'm surprised that the top plate of the CCU has been removed although the hole sizes would be the same and the IP rating when the front cover is replaced fullfills IP4X. Glanding off the SWA is not a problem if it is done before the board is fitted. The SWA is/was used, I presume, with supplementary bonding in place and to aviod the necessity to fit RCDs and also assumes this lnstall was completed before the 18th ed.
Is this really a C2? C3 max and a note regarding the lack of RCDs

Taking all things wrong with the install into consideration i say C2.
Tha angle which swa enters means that the connections are under stress.
Theres alot of dust inside the consumer units due to the large hole. Theres a draft so anything could enter it etc insualtion...
I believe c2 also for the lack of rcd protection due to them being in a commercial premesis and not being used for fridges in all cases also not labelled and no RA.
I stick to my original coding.
 
Don’t insult my intelligence please , “the fact I was unaware “
Clutching at straws.
If it was required at the time it would have been in the regulations.
Double pole fusing was once a requirement, how did that one go?
So you must be stating that you’ve always installed wiring systems against premature collapse?
Ever since you’ve been an electrician you’ve always installed metal fixings to hold the cable in place inside trunking?
I have never, to this day used metal fixings inside trunking to hold cable in place.
Never had the need to.
 

Reply to Poor install EICR 12 year old hotel in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top