welshmadness

Hi guys.
Anyone know of a good web site or formula to work out what Kvar value is required for a 3 phase 4pole inductive motors?

Thanks :)
 
Sorry mate:confused:


Power Factor


The Power Factor of your electrical system can cost you money. A low Power Factor will cause your utility company to add a penalty to your electric bill, and your increased system losses will turn electricity into wasted heat, shortening equipment life.

The Sales Engineering staff at Kele often receives calls concerning Power Factor. Some of the calls are for application assistance in choosing Power Factor monitoring equipment. Other calls come during start-up with questions about the validity of watt, current and voltage measurements that are affected by Power Factor.



What Is Power Factor?
Power Factor (pf) is the ratio of real power to total power. Real, or productive power, is the actual power used in a building, measured in kilowatts (kW). Reactive power generates the magnetic field for inductive loads such as motors, transformers, lighting ballasts, etc. Reactive power is measured in kilovars (kVAR). Total power (measured in kVA) is a combination of real power and reactive power.

The basic formula for Power Factor is the mathematical ratio of real power to total power. This ratio is an effective measure of system electrical efficiency and is represented as a percentage or decimal (e.g., 90% or 0.9).



Other Power Factor Calculations

[ElectriciansForums.net] Power factor capacitors

Graphically, the Power Triangle on a system would look like this:

[ElectriciansForums.net] Power factor capacitors

The relationship between kVA, kW, and kVAR is as follows:

*kVA2= kW2 + kVAR2 or VA2 = W2 + VAR2

Thus, with substitution, another formula for power factor could be derived:

[ElectriciansForums.net] Power factor capacitors

On a single-phase circuit, the current will usually lag behind the voltage. The amount of the lag can be measured in degrees (360° for one complete cycle). The cosine of this phase angle also equals the power factor.

[ElectriciansForums.net] Power factor capacitors




Effects Of Power Factor

System Capacity - Your kVA is the total power available. Your useful power kW = (kVA)(pf). The higher the system power factor, the more system capacity that is available. With more system capacity, voltage will remain more stable as loads are cycled on and off. Also more load can be added to the system as needed.
System Losses - With a higher Power Factor, less current flows through your system. There is less power lost (I2R losses) to heating of cables, bus bars, transformers, panels, etc. These devices will run cooler and last longer too.
Utility Charges - Electric utilities must maintain a high Power Factor on their distribution system for efficiency. They will typically bill customers for a low Power Factor or they may bill on kVA demand, which Power Factor will affect. Most utilities that bill a Power Factor penalty require a user to maintain a 95% Power Factor to avoid penalty.



Power Factor And Motor Loading



[ElectriciansForums.net] Power factor capacitors


Power Factor is affected significantly by motor loading. Figure 1 represents a typical T-frame motor curve. It is evident that the highest Power Factor is at full loading. Since this Power Factor will affect the system Power Factor, proper sizing of motors is important. Over-sizing motors will lower the system Power Factor. Understanding motor efficiency and Power Factor is important in building automation. As you can see, your control scheme for the loading of chillers can affect your power usage.
Frequently we get calls on chiller applications using watt transducers. The installer believes the watt transducer is reading low, compared to voltage and current measurements. We usually find the chiller is only partially loaded and the Power Factor is low (e.g., 48% pf at 25% loading).
The addition of capacitors or the use of high efficiency motors will improve the Power Factor. Application of capacitors at the right locations and precautions involving electronic equipment need to be considered. High efficiency motors are more expensive but have a higher Power Factor.



Power Factor Correction

Capacitors are typically added to a system to increase system Power Factor. Some users install switched capacitor banks at the incoming service for utility bill savings only.

Since capacitors only improve a system from the capacitor back to the power source, many users will install capacitors at motor loads so they will be switched with the motor. With this method the benefits of lower *(I2R) losses improve their whole system. The addition of variable frequency drives will usually improve the Power Factor.



Measuring Power Factor

There are several methods to calculate Power Factor. The method is usually determined by the math capabilities of the automation system. If a watt transducer is used with a voltage and current transducer, the following formula is used:

[ElectriciansForums.net] Power factor capacitors

If a VAR and Watt Transducer are used, the following formula would be used:

[ElectriciansForums.net] Power factor capacitors

If a phase angle transducer is used to determine phase angle, then the following formula is used:

pf = Cos Ø

Kele offers a full line of Power Factor monitoring equipment, along with our other power monitoring products. Call our Sales Engineers for application assistance.

[SIZE=-1]* This equation contains subscripts or superscripts which may not be supported by all web browsers. Contact your Kele Sales Representative if there are any questions about this formula. [/SIZE]Here it is:confused:
 
Last edited by a moderator:
Electrical Engineering Calculators

Try above link a bit of subject but has some useful calculators none the less :)

nice post Mac takes me back a bit :D

Positive reactive volt-amps represent VAr and Negative reactive Volt_ampperes represents leading VAr

Power Factor

Cos Ø = P/ EI = kW/kVA

Current

active components = I cos Ø

reactive components = I sin Ø


:cool:
 
Last edited by a moderator:

Reply to Power factor capacitors in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Hello, Last year my 30 year old Static Pase convertor stopped working, the 3 phase motor is 0.55KW / 0.74HP and drives a small lathe. When I...
Replies
0
Views
186
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top