Safe isolation - make sure you know this e.g. turn off the correct isolator to the board padlock with sign through the lock and !!Key in pocket!! (this is a big fail for some ppl) prove your tester then do your 10 tests (main cables come in/before breaker) L1-L2, L1-L3, L2-L3, L1-N, L2-N, L3-N, L1-E, L2-E, L3-E, N-E then re prove your tester and make sure you ask assessor before starting installation
Installation - not exactly sure what circuits you have to do but everyone should be capable I think its gas and water bonding, 2 way and intermediate light circuit using twin and earth and 3 core, Ring Main - 2 sockets a fuse spur(boiler circuit) spur socket in singles, boiler circuit - but your just attaching feed to spur, smoke detector to un switched fuse spur then FP200 to detector, commando socket in SY cable, motor circuit in Armoured cable I think it’s to direct on line starter which is already wired then to motor not sure what type of cables and am no expert in motors find it to boring but I think you have to use (P = (Square root of 3) X 3 X I) to set the motor and would also use it in fault finding oh and 2 telephone points you have to wire between
All circuits have relevant diagrams and information
Just make sure all cables are terminated correctly and tightly any come loose and it’s a fail
Testing
Not going to much in to detail will be here forever
make sure you ZERO leads on continuity of CPC and Ring Final and if you go off and ever go back to it or if you swap over to plug leads
Don’t forget R2 method for gas and water bonding
Polarity- make sure you switch your switches and socket and whatever else
Insulation Resistance make sure all sensitive equipment is removed e.g. lighting circuit remove cables from fitting put in connector blocks, smoke detector should be like a block that you can pull out of the detector, boiler circuit pull the fuse out of spur, motor test your installed cables not through the whole circuit and don’t forget about testing through your strappers
Make sure the installation is but back together during insulation resistance e.g. switches screwed back and containment back together cos this is a fail
When finished insulation resistance put everything back together and ask if you can energise the installation
You have to prove you have a supply and phase rotation is correct same with commando and motor
Then turn main breaker off and test incoming side/before breaker for your ZE and PFC make sure do each phase to N and E and press PFC button in-between as well record highest reading (presuming you have the new type of Megger)
You don’t have to do the earth fault loop impedance test just add your ZE to relevant R1 + R2 (Zs = Ze + (R1 + R2)) and record check your calculation with that on page 103 (table 2D) of on site guide (not the regs as the table in regs doesn’t account for the 80% that you have to be within where as the OSG does)
RCD test and function test
Don’t forget to use GS 38 tips when the installation is live
FAULT FINDING
This includes the whole installation well not actually yours will most probably be the same installation but on a fault finding test bay which your assessor will switch certain switches thus putting faults on the installation
You should look out for using low ohms is
OPEN CIRCUIT
CROSS CONNECTION
and insulation resistance
SHORT CIRUIT
The best way would be to eliminate the Neutral and earth path first and then concentrate on the live paths
I don’t think there should be faulty equipment but don’t bank on this but there may be like a broken fuse or something so simple you just can’t see it
Be technical as well don’t just say found it live on the light don’t work say something like - on the lighting circuit there is a an open circuit on the S/W between common on the light switch and live on the light fitting or cross connection on the lighting circuit between the l2 strapper and the common in the second 2 way switch.
As of paperwork make sure you can fill out pages 332, 333, 340 and 341 of BS7671 17th edition
Assessment of Applied Knowledge
This is a 30 question multiple choice exam(4 answers) and these questions can be tough I’m not sure what the pass rate is but try and get everyone of them right you can’t take your own books in but you get a copy of the Regs , On site guide, Guidance note 3 and the Electrical installers' guide to the building regulations its probably worth getting the books and having good understanding of the books I think it’s an hour long so you only get two minutes a question
Always remember your assessor will not try and trick you this isn’t your driving test they will want to pass you they can’t tell you what to do or give you too much help but they may show signs of body language or they may ask if you’re absolutely sure you’ve finished remember to be calm and take your time concentrate on everything
Good Luck and hope this as some way helped you
I am not an expert so I would only take this as a guide I am only going over what I think is important points I am not affiliated with the AM2 board I am not a teacher or an assessor I have no accurate information on the exam, all of this guide I have wrote through experience other people other websites, Please don’t mock what I have wrote I’m only trying to help people like I said I’m not an expert I might have said something and it not be correct if I have missed anything feel free to mention it and also if any one as any questions. As you all should be able to tell I wasn’t very good at English lol
Thanks for reading