What voltage did you have on the Switched live when it was supposed to be off?
I tested with a Fluke T120 Its not supposed to give a LCD readout below 12 volts but if I switched the light switch on it read 247v and when off it went down the scale and rested at 9 v. I usually just get red lights illuminated and a buzzer at 12 volts on the scale on the meter. Which tells me its less than 12
 
Hi - thought was to try a small load from SL to N at the fan. Purpose is to clamp off SL to zero volts when light switch is open. It will only have effect if there is leakage through the switch or induced voltage from other cables. Good hunting !
 
My Fluke 110 gives me or sorts 'low' voltage readings, which I don't believe in :). Have you tried measuring this 9 volts with an analogue meter, before you get led up the garden path?
 
You've ruled out the fan as being the problem as far as I can see, so now you need to track down where the this 9V is coming from.

What have you measured the 9V with reference to, earth or neutral?
if you have a suitable multimeter then try measuring it with that, I suspect it will give a higher voltage reading.

I think the simplest explanation for a voltage on the S/L when it shouldn't be is that the switch is not operating correctly, so I'd be inclined to test that first.
 
If the voltage actually exists, as well as checking the switch, the remainder of the circuit (i.e. in other rooms) needs to be verified that its wired correctly. I had to fix a fault, where live had been connected into neutral and neutral vice versa.
 
methinks all threads regarding timer fans should themselves be on a timer, and self-destruct after 2 days.
 

Reply to Problem with a timer fan on light circuit in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
200
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
672

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top