Problem with PSSC on three phase supply | on ElectriciansForums
Discuss Problem with PSSC on three phase supply in the UK Electrical Forum area at ElectriciansForums.net
sparksburnout
Nearly Esteemed
Notts
I have a domestic premises (it was once a shop) that has a three phase supply, although only one is being used now. I am using a di-log 9083P tester, and when doing a Ze test am getting 23KA as the reading for PSC, with 0.01 ohms as the loop resistance. I am getting a Ze of 0.35 ohms and a PFC of 565A. The values for PSC and L-N loop impedance seem unbelievably low to me? I am not sure where the local transformer is but it is not next door, I think it is about 400yds away. System is TNS. I have looked at the thread in the I&T forum, and used the method of inserting an impedance in the earth lead of the tester, but I am still getting the same readings, which as far as I can see you would, as it is for low Ze not low PSC. I have used the tester on about 3 other installations, and it is giving expected results. Could it be possible that these values are correct? In which case the main switch and breakers are well underrated!!
just check your readings again will you on Zpn....caus 23KA ffs....
I know! I just tried it again over the road at my mates house, and it's giving very similar readings now - the previous ones I mentioned were Zs. This meter is quite new, I suppose it could be faulty, or is it that these meters are just not capable of working properly at low Ze's? It is still giving a P-N loop res of 0.01 ohm that can't be right even if the transformer was next door???
Hi if I leave my megger in the van over night when it's cold I get strange pfc and loop readings I leave it inside in the warm for a hour works fine it has been calibrated a few times now with out any problems,had me scratching my head at first
it can be 0.01, thats what it is at the factory i work at
Reply to Problem with PSSC on three phase supply in the UK Electrical Forum area at ElectriciansForums.net
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!