Depends. If it is 16mm 2-core SWA then R1 = 1.15 ohm/km, and R2 = 3.7 so for about 10m that is 0.049 ohm. If 3-core then R1=R2 = 1.15 so R1+R2 about 0.023 ohm.
For NYY-J 6mm it is about R1 = R2 = 3.08 so 0.019 ohms for 3m.
Working backwards from 0.28 for 32A D-curve we have:
- 2-core Ze max = 0.28 - 0.019 - 0.049 = 0.21 ohm
- 3-core Ze max = 0.28 - 0.019 - 0.023 = 0.24 ohm
Both are quite low. If you are TN-C-S you might meet them (assuming your PSCC at supply is a bit over 1kA) but probably not if TN-S (and no way TT). Measuring the current workshop CU Zs & PSCC would be the best starting point.
As
@timhoward has already pointed out a fused-switch for 32A is much easier to meet, but check the manufacturer's data on what fuse(s) are acceptable.
If there is no way other than an RCD for meeting disconnection then one option for higher reliability, not the cheapest, is to have a 100mA delay RCD on the sub-main supply and a 30mA 'instant' for the socket outlet. That way you would still disconnect in under 0.4s even if
one RCD was faulty. However, depending on how it comes from your main house CU that may (or may not) be easy.
You don't need the usual additional RCD protection on SWA cable even if it is buried or hidden in plaster (assuming armour is earthed as it should be and it meets 5s disconnection) so if you have a non-RCD 63A C-curve feeding a separate RCD enclosure to feed the sub-main, you could change that for a 100mA delay and then have a 30mA one in the workshop CU for shock protection.