Hi, does anybody know what other brands of MCB (if any) will fit an axiom consumer unit? I need a C32 breaker but i cannot source axiom C curve breakers anywhere. The initial problem is my Plasma cutter trips the B32 breaker as soon as I touch the trigger, and i cant think what else the problem could be.
What sort of plasma cutter is it?
e.g. 3/8 " cut?
Axiom is one of the cheapest consumer unit brands aimed entirely at the domestic market that rarely needs type C breakers, and I'm unfortunately not aware of any source or anything compatible.
Some people find these units work ok, but I avoid them after having had two units with faults in a row.
Before entering a world of pain trying to modify the supply I'd try the plasma cutter on a different installation and prove the issue is the inrush current as you suspect.
e.g. 3/8 " cut?
its a 40mm cut, ive just checked the manual and it recommends a D32 breaker, so im going to rip out the Axiom consumer unit and replace the whole lot with Hager
Remember that a D32 is unlikley to be suitable for a domestic ring circuit supplying general purpose sockets.
it MAY be suitable for a dedicated supply for the cutter but it would have to be calculated. This is not an arrangement that is part of the standard circuits Of the on-site guide.
its only suppyling the plasma cutter and welder both on individual 32a sockets and both supplied by 6mm NYYJ from the consumer unit.
Im planning to use D32 for the 32A sockets (6mm NYYJ), a C32 for the workshop ring main (2.5mm T+E), C16 for the 110v transformer supply (1.5mm NYYJ) and B6 for the lighting. Unless anyone can see any problems?
These changes could impact the ability of your installation to turn itself off within required disconnection times under fault conditions.
e.g. A D32 breaker will only turn off within 0.4s if the total earth loop impedance is less that 0.27 ohms, and no electrician would say over the internet that this is likely or can be assumed, in fact it's unlikely.
My house has a higher earth loop than that at the consumer unit before the resistance of the circuit.
While you have a good grasp of what is going on you need some testing doing.
A pertinent question is whether you have RCD protection for these circuits.
Without getting into it in depth this affects possible reliance upon RCDs for fault protection, and a new regulation since 18th about <=32A sockets requiring RCD protection.
yes, the workshop consumer unit is fed from the main house consumer unit via a 63a RCD then C63 MCB, and 16mm SWA
As much as I don't like relying on RCD for disconnection times, if you find you can't meet the Zs for a 32A D-curve (something like 0.28 ohm from memory but CHECK THAT) then having an RCD would allow you to achieve < 0.4s for L-E faults (the only ones where ADS is specified).
As this ought to provide over-current protection for the cable you should have no other worries so long as it is meeting voltage drop.
Having separate RCD for those circuits would make sense as well, as I suspect a high chance of tripping the whole house (or half of it) otherwise!
The one thing I wouldn't do is just bung a D32 in. This needs a sparks, and not a domestic-only one.
My top few questions if I was on site, considering the 'simple' option would be:
-What the Ze at origin is and Zs at the workshop are
-How the trip curves of a D32 in workshop and upstream C63 in house compare and which one would operate first, at what time/current
-Whether the Zs forces me into RCD protection for fault protection, which isn't good practise as RCD are much less reliable than fuses/breakers
-Am I happy about the RCD for fault protection (if required) being at the house, and the house also turning off in fault conditions.
-Are the cables sized correctly for an L-N fault protected by a D curve breaker
Or:
-Whether converting to fused sub-main for workshop, and fused permanent supply for plasma cutter was more appropriate and allowed me to stay within max Zs value of the OCPD, and have a local RCD for additional protection.
The answer is almost always "both at once, and when you least want it".
Unless both CU are from the same maker (e.g. Hager) you won't get selectivity information as manufacturers usually only give it within their own ranges (and even then, not always!) and with BS88 fuses or similar.
I would advise the OP to have some emergency lighting just in case it all trips and goes black when in the middle of doing something hot and dangerous. (Sadly not that sort of hot and dangerous)
Devon
Electrical Enthusiast (Unqualified Hobbyist etc)
Problems with Axiom MCBs
big chaz,
pc1966,
TrueNAS JBOD Storage Server