Jon Hodgson
Hi guys I'm after a bit of help with working out my Max Demand normally in a domestic situation its fine but theres so many heaters and water heaters on this that I'm a bit confused.
I have been asked to do a bit of commercial installation for a kitchen and toilets its a children's soft play center.The installation calls for hand dryers and instantaneous water heaters.
Landlord is installing the supply for the space this has been done already without any consultation about the max demand. At present I'm unsure as to the max load of the incoming supply yet but its only single phase and from the calcs Im worried that its not going to be man enough for the job.
They have however brought in a 4 Core SWA so theres the potential for a second phase to be installed or another supply from the same phase. Its a big commercial complex so hopefully shouldn't be a problem I had expected three phase though.
Client is supplying all the equipment I have not had all the information for the machines going on the ring main though so blanket 32A
Hopefully the wattages are correct on the information I have had
Having done the calcs the Demand From reading Appendix A I have come up with the following.
Heating and Power
Hand dryers - 2 @ 1.7kw & 2 @ 0.9kw Total 4325 w = 18.8A
Ovens - 1 @ 4.7kw 1 @ 2.1kw = 30A
Ring Main - Dishwasher, Coffee Machine, Slush puppy machine, Ice cream machine, PA system / Music CCTV = 32A
Fridge & Freezer Approx 3kw = 13.1A
Lighting - 3.5kw total = 13.7A
Instantaneous Water Heaters 1 @ 5.5kw 1 @ 4.5kw = 43.48A
Undersink heater 1 @ 2.7kw = 11.7 A
Total of 162.78 A
This seems rather High. Odds on that everything is never going to be on at once.
Hand dryers and instantaneous water heaters make a total 62.28A if all are on at once.
Any advice/corrections/suggestions would be greatly appreciated
I have been asked to do a bit of commercial installation for a kitchen and toilets its a children's soft play center.The installation calls for hand dryers and instantaneous water heaters.
Landlord is installing the supply for the space this has been done already without any consultation about the max demand. At present I'm unsure as to the max load of the incoming supply yet but its only single phase and from the calcs Im worried that its not going to be man enough for the job.
They have however brought in a 4 Core SWA so theres the potential for a second phase to be installed or another supply from the same phase. Its a big commercial complex so hopefully shouldn't be a problem I had expected three phase though.
Client is supplying all the equipment I have not had all the information for the machines going on the ring main though so blanket 32A
Hopefully the wattages are correct on the information I have had
Having done the calcs the Demand From reading Appendix A I have come up with the following.
Heating and Power
Hand dryers - 2 @ 1.7kw & 2 @ 0.9kw Total 4325 w = 18.8A
Ovens - 1 @ 4.7kw 1 @ 2.1kw = 30A
Ring Main - Dishwasher, Coffee Machine, Slush puppy machine, Ice cream machine, PA system / Music CCTV = 32A
Fridge & Freezer Approx 3kw = 13.1A
Lighting - 3.5kw total = 13.7A
Instantaneous Water Heaters 1 @ 5.5kw 1 @ 4.5kw = 43.48A
Undersink heater 1 @ 2.7kw = 11.7 A
Total of 162.78 A
This seems rather High. Odds on that everything is never going to be on at once.
Hand dryers and instantaneous water heaters make a total 62.28A if all are on at once.
Any advice/corrections/suggestions would be greatly appreciated