Had this two weeks ago in a fire damaged bungalow. I know it sounds implausible to some but a neutral to earth fault on a circuit stopped the RCD from tripping and test button wouldn't work. Dissed circuit in question...RCD now tests fine and test button works.
 
You will more than likely get a higher Zs through an RCD due to it's own resistance and also the test meter puts out a lower current on the no trip setting so the result isn't as accurate.
 
Right i recon i have a n earth fault on a lighting circuit on that side of the red and also a crossed n on the other

I recon this is my problem hammy

Any ideas on the different zs values I'm getting from my dialog tester on the same socket chaps ?
 
@Loki 2.5 T&E RFC with a R1+R2 reading of 0.48 would give an expected value of 1.15 for r2 and 0.77 for r1.

1.15+0.77= 1.92

1.92/4=0.48

To work it out

0.48x4=1.92

1.92/1.67=1.15 for r2

1.92-1.15=0.77 for r1
 
You said that the Ze is 0.5
Im guessing its a tns & not tncs then as its over the 0.35 Ze max



If using 2.5 (1.5) T&E

Zs 0.98 - Ze 0.5 = 0.48

4 ÷ (2.5 + 1.5) x 0.48 = 0.3

r2 = 0.3 ohms
r1 = 0.18

Roughly lol, Am i close?
You said that the Ze is 0.5
Im guessing its a tns & not tncs then as its over the 0.35 Ze max



If using 2.5 (1.5) T&E

Zs 0.98 - Ze 0.5 = 0.48

4 ÷ (2.5 + 1.5) x 0.48 = 0.3

r2 = 0.3 ohms
r1 = 0.18

Roughly lol, Am i close?
Are you answering post 3?
 
I seem to recall, I might be wrong, one of our more eminent members describing a situation where a neutral earth fault on a circuit could trip an RCD that is not protected by?
 

Reply to problems with test results in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
785
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
421

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top