Thanks guys i think i got the hang of it now, your help is much appreciated. The duel display actually shows Ze & PFC at same time, there is no 'PFC' setting as such, so testing for PEFC I have to do a Ze test but with the earthing conductor connected to the met, ignore the Ze result and just look at the PFC reading. Same with PSCC do a Ze between L-N incoming and read the PFC result :)
 
Hi

Recently brought 1710;Having the same problem with loop settings.Please could you advise me whether these settings are correct as i am new to testing >llearned on 1500 series and these new loop settings have thrown me a bit.Thank you in advance

Angus
 
Hi any advice would be nic

There's 2 options in Loop
L-PE with a sub category 3Lo, 2Hi and 2Lo
and L-L/L-N which is a 2Hi test

Here is what I think are the correct settings
Ze - L-PE on 2Hi
PSCC - L-N on 2Hi
PEFC - L-PE 2Hi same as Ze
Zs - L-PE on 3Lo

any help would be appreciated x

I bought a Megger 1730, then went on 2392 and used a a 3 wire Kewtech MFT. I had (and to some extent still have) the same confusion. I emailed Megger and recieved this reply: To conduct an external loop, PFC and PSSCtests on your MFT1730 please note the following:

Firstly all the tests should be 2 wire highcurrent only.

The second dial should be set to ‘Z’

Large dial on L-PE range with 2Hi rangeselected

For a Ze measurement the red and greentestleads are connected phase to L1 (MFT terminal) / main earth terminal to L2(MFT terminal)
The PFC measurement is displayed at thesame time above the loop / Ze measurement.

For a PSSC measurement move the green prodfrom the main earth terminal and connect to the neutral bar. This will give aL-N loop test with the PSSC measurement displayed above.

3Lo has been designed for circuits with an RCD, therefore not applicable to Ze at origin, unless you have a slightly complicated distribution. Clearly your 1710 dials are different to the 1730, why don't you email Megger for clarification. They are quite helpful.
 
Angus the settings i stated work well for me, what threw me was the fact that whilst doing a PFC test there is a 'Ze' measurement on the screen. This is because of a duel display hence the lack of PFC setting on the dials
 
Thanks guys i think i got the hang of it now, your help is much appreciated. The duel display actually shows Ze & PFC at same time, there is no 'PFC' setting as such, so testing for PEFC I have to do a Ze test but with the earthing conductor connected to the met, ignore the Ze result and just look at the PFC reading. Same with PSCC do a Ze between L-N incoming and read the PFC result :)

Most meters show loop/PFC on the same setting...
 
I think Megger tried to be too clever rushing out the 1700 series with all its new tricks their 1500 series worked so why change it
 
Most meters show loop/PFC on the same setting...
all of the meters 1500 series do not show loop/PFC measurement though which were standard issue for everyone in my classes. So it's new to me when they combined it, personally i preferred a different setting but there you go.

yes oldtimer I agree it wasn't broke so why try and fix it!
 
all of the meters 1500 series do not show loop/PFC measurement though which were standard issue for everyone in my classes. So it's new to me when they combined it, personally i preferred a different setting but there you go.

yes oldtimer I agree it wasn't broke so why try and fix it!

Yep I understand if it was an improvement but remember Megger's big selling point was you could do a 2 wire Zs test at a light switch when the regs was saying you had to test at the light point as this was the true end of the circuit.

So why did I buy the 1553 well because at the time Fluke's 1600 series was having problems I shoul have bought the 1552 as the bluetooth for me was a waste of time plus my biggest bug bear was that stupid carry case banging against my legs when going up stairs plus it had no storage. So I bought a Fluke carry case and it was the best buy I made for £28 great storage for the leads and bits and bobs.

Mind you Megger guy was not happy about it but I told him well if you ignore your customers then I will carry my 1553 in a Fluke box lol
 

Reply to Problems with testing with a megger 1710 help! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
605
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
390
Megger 15 series in my opinion are the best. Had a few 17 series that have put out err 23 codes. This is s an internal clock component issue...
Replies
2
Views
401
Darren dazz
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top