after my rather vague thread Friday about finding the 30 mtrs of 10mm 2 core swa In the back of me van.....after some views on earthing to the shed, 3 options as far as I’m aware are
1. Run a single 10mm from main met upto the shed and use that
2. Use the armour of the swa, adiabatic permitting..
3. Connect the swa to the main met at source end and TT the shed
Each option is appruthe same cost wise and it’s my own house so Labour is not a big issue, as per title just after others views and preferences....
 
Hi - just FYI, from GN8 I read that 2 core swa 10mm has actual steel of 26mm (table B2). Since you only need 22mm (ish) steel to equal 10mm Cu (for thermal effects for 70C cable) then it’s fine.
Not sure, but your 41mm figure could be from 4 core 10mm cable?
 
Last edited:
Hi - just FYI, from GN8 I read that 2 core swa 10mm has actual steel of 26mm (table B2). Since you only need 22mm (ish) steel to equal 10mm Cu (for thermal effects for 70C cable) then it’s fine.
Not sure, but your 41mm figure could be from 4 core 10mm cable?
There are 3 different types of SWA cable.
70 degree C PVC 2 core 10mm2 BS6346 SWA has a CSA of 40mm2, and a value for K of 51.
90 degree C PVC 2 core 10mm2 BS5467 SWA has a CSA of 26mm2 and a value for K of 46.
90 degree C XLPE 2 core 10mm2 BS6724 SWA has a CSA of 26mm2 and a value for K 46.
 
When calculating the CSA of a protective conductor, using tabulated values, you use the tabulated values.
If you were calculating using manufacture’s data, you would use their values.
 
Last edited by a moderator:
There are 3 different types of SWA cable.
70 degree C PVC 2 core 10mm2 BS6346 SWA has a CSA of 40mm2, and a value for K of 51.
90 degree C PVC 2 core 10mm2 BS5467 SWA has a CSA of 26mm2 and a value for K of 46.
90 degree C XLPE 2 core 10mm2 BS6724 SWA has a CSA of 26mm2 and a value for K 46.
Hi - so are you saying that GN8 is wrong or that I’ve read it wrong? :) .
 
Last edited:
Good question pretty mouth, havnt used the adiabatic in real life scenario before so just went through my notes, this was a good opportunity to do some calcs and get the brain working agian as it’s my own property, I will be redoing it all this evening but as Andy points out it’s all a bit academic as we nlkniw the csa anyway.......possibly maybe :)
 
Hi - no questions can be stupid :) .

My thought is - the actual steel in 2x10mm swa is at least 26mm which when converted with the appropriate temperature rise k factors is equivalent to more than 10mm copper so it’s going to be ok for CPC. As you say, no real need to look at the adiabatic equation for that circuit.

Happy to have feedback if I’ve got this wrong :) .
 
Am I missing something here?
If you know that the cpc is 26mm, why do you need to do the adiabatic?
Apologies if I'm being stupid.
If the CSA of the Steel Wire is 26mm2.
It’s not a given that the copper equivalence will be sufficient.

Here’s a link to a chart produced by John Peckham, for at a glance checking the CSA of the Steel Wire is sufficient:
Use SWA as CPC, a guide to the acceptability of steel wire armour use as CPC. - https://gadsolutions.biz/regulations/swa-as-the-cpc

Sure this has been posted in the past.
 
Baddegg, my experience of the adiabatic is limited too, hence the question. Just about getting my head around it now though, i think.

Charlie, the name Pretty Mouth comes from the movie Deliverance (my favourite romantic comedy), what makes you so sure I'm a boy? Haha
 

Reply to Pros...cons...preferences.. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
386
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top