Hi Guys

How do you calculate Prospective Fault Current??

Wouldi be correct in thinking it is nominal voltage divided by Zs + R1 + R2 ???

So

Nominal Voltage
Zs + R1 + R2

A
 
You are looking a little confused.

Ze = external earth loop
Zs = Ze + (R1+R2)

Your highest PFC will be at the origin of your installation thus PFC = Uo(Nominal Voltage)/Ze


(off the top of my head and hopefully correct :eek: )
 
Ok

Well i think ive calculated it right. measured Earth loop Impedance is 1.08. my r1 + r2 = 0.05. So ze = 1.03 so..

230/1.03= 223.3 ka..

Yup Pretty poor earth.

But this is a college test fortunatly and main protective conductor is only small as the circuit isnt used to power anything simply for testing purposes.

Cheers Guys

A
 
If you not got Ze

Ze =Zs-(R1+R2)

Not necessarily as parallel earth paths (water or gas bonding for example) can bring the overall Zs measurement down thus hiding a potentially higher than acceptable external impedance.

By all means, calculate Zs but never back calculate Ze.

To the OP:

Also, remember that PFC is the highest figure of PEFC (prospective earth fault current - Line to Earth) or PSSC (prospective short circuit current - Line to Neutral).
 
Last edited by a moderator:
Ok

Well i think ive calculated it right. measured Earth loop Impedance is 1.08. my r1 + r2 = 0.05. So ze = 1.03 so..

230/1.03= 223.3 ka..

Yup Pretty poor earth.

But this is a college test fortunatly and main protective conductor is only small as the circuit isnt used to power anything simply for testing purposes.

Cheers Guys

A

Not 223.3 ka but 223.3 amps or 0.223 ka
 
Not necessarily as parallel earth paths (water or gas bonding for example) can bring the overall Zs measurement down thus hiding a potentially higher than acceptable external impedance.

By all means, calculate Zs but never back calculate Ze.

To the OP:

Also, remember that PFC is the highest figure of PEFC (prospective earth fault current - Line to Earth) or PSSC (prospective short circuit current - Line to Neutral).


When measuring Ze you must do so with the main earth disconnected so that no prarallel paths interfere with the reading, however, measuring PEFC you do with all Earths connected to include Parallel paths because you are looking for the lowest Earth Impedance reading and hence the Largest PEFC reading.
 
My point was that you can't calculate Ze, not the ins and outs of measuring PFC of which I'm fully conversant with.


Your post was a little confusing. I was just trying to clarify for people who aren't as 'Conversant'
 
What if the incoming earth has a fault and PEFC is high due to parallel earth paths from the water and gas supplies?
Zs may well be fine but an underlying problem could go amiss.
 
GaryM is correct - you can't accurately calculate Ze using other measurements
(eg Zs, PEFC) as these measurements are taken with the main earthing
conductor connected (parallel paths), giving a lower Ze than it would
actually be.
As stated earlier, Ze is measured with the main earthing conductor
disconnected and is pretty much impossible to calculate accurately:)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Oswestry

Thread Information

Title
Prospective Fault Current
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
Ashley Williams,
Last reply from
Guest123,
Replies
31
Views
26,839

Advert

TrueNAS JBOD Storage Server

Back
Top