Protective conductors on an EIC | on ElectriciansForums
Discuss Protective conductors on an EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Afternoon all.
Can I confirm that a protective conductor in section 16 of an EIC refers to bonding to services etc rather than a cpc of a final circuit?
It's under schedule of items tested.
If you mean "presence of protective conductors" if you look closer it also ask about presence of Earthing and bonding conductors protective conductors mean cpc.
Can you state what it actually says along with any Reg Nos if applicable as I have no idea what the Easycert formats contain.
See line 13.3 on picture.
The distribution board that this cert refers to does not have any main protective conductors to supplies. So I was asking in your opinion this means cpc for final circuits or just main protective conductors.
[ElectriciansForums.net] Protective conductors on an EIC
Different to the form I looked at
Protective conductors would cover circuit protective conductors (cpcs) and the earthing conductor at source of supply. As there is no mention of main protective bonding conductors it probably includes these as they are also protective conductors.
Reply to Protective conductors on an EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A lot of external bonding or earth conductors are bare copper strips. If mechanical damage is likely, then run some steel conduit… but all UV...
It's true. Prior to a lightning strike, a charge is buikt uo between the earth and clouds - very much like charging a capacitor. Wgen the field...