Hi guys, I have a starter rated 440v, and wanted to use it to a pump rated at 220-240 delta/ 380-415 star, is it possible to connect it in delta? or it should only be star?
Discuss Pump Control in the Talk Electrician area at ElectriciansForums.net
For the OP, you also asked about how you should start the Motor, you need to take in lots of variables, mechanical loading for example, starting currents etc many things need to be considered.What's your supply voltage is more importaint.
An what do you mean rated at 440V? As in that's the maximum voltage the starter will take?
What kind of starter is it?
Yup, you're right, sorry 'bout that, supply voltage's 400V, star indeed.. Thanks mate! Just wanted to confirm before doing it.You will have to run in star. However the voltage is still a bit high.
Would be better with a VSD that you could trim the output to what you require.
Manual for soft start is here:
I should add, you're starter isn't rated at 440v it's 380 - 415 V.
What is your supply voltage?
Reply to Pump Control in the Talk Electrician area at ElectriciansForums.net