I would be recommending replacing the front end 30mA RCD with a 100mA and installing RCBO's for the socket
This is a 16th edition board and is original to the property. I am not asking on advice on how to bring to the 17th. I am asking why there would be a short between the service neutral and my TT earth. Can anyone shed any light on this as the distance to the transformer is quiet a way And thus should not pick up resistance to the earth point there. Has anyone had this before.
Thanks anyway murdoch.
Maybe not, but this is the second occasion you have been to this installation, and you Have previously carried out installation work to the property. A CU change would have been prudent advice to the customer at that time, rather than 2 years or so down the line. So when you do upgrade the present CU, replace that up front 30mA RCD with a 100mA S type, to give extra protection without nuisance tripping to this TT installation. A straight 100mA RCD will not work, most faults will take out both the 30mA and the 100Ma RCD's....
As for your problem, it's just a case of breaking things down and testing until you can isolate where the connection lay's. Only methodical testing is going to reveal or point you in the right direction as to the cause!! Conduct a ramp test to find out, at what sort of leakage current is taking the present 30mA unit out.... Do you own/posses an earth leakage clamp tester??