Brian, do you think your 17.6kWh of gas saved daily is a bit optimistic? For example, how many kWh has your Immersun indicated that it's putting into the HWC each day? The reason I'm asking is that I'm wondering how inefficent (in terms of gas energy to energy in hot water) the indirect gas water heating is. Certainly a modern condensing combi boiler can manage 80%+, but it is directly heating the water so I was sort of assuming that a modern condensing system boiler would be making 70%+ after allowing for heat loss in pipes to the HWC etc. But this would still mean that 17.6kWh should be more than enough to fully heat the HWC from cold twice a day. Energy to heat water in Wh at 100% efficiency = 1.16 x number litres x temperature rise, so 130 litres through a 35 deg temp rise = 5.28kWh. The immersion should be close to 100%.
Mike
We've fitted several Immersuns now, though a couple of the customers needed rewiring as they had other stuff connected onto the immersion circuit. I've one fitted at home, but it is only heating a towel rail - we have a combi - currently planning to have a thermal store fitted, unless anyone has a better idea.
Mike
We've fitted several Immersuns now, though a couple of the customers needed rewiring as they had other stuff connected onto the immersion circuit. I've one fitted at home, but it is only heating a towel rail - we have a combi - currently planning to have a thermal store fitted, unless anyone has a better idea.