How is a 6A MCB with a shunt trip going to hold a contractor open?
It it will hold it closed sorry, then when triggered it will release the contactor and shut the PV end off.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Pv on rcd in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
How is a 6A MCB with a shunt trip going to hold a contractor open?
I have to say this is a really interesting thread!
if we need to disconnect both ends, how about this.
from the main db, circuit starts with an RCBO, then connected to that would be a 6A MCB on a shunt and that circuit holds open a NO contactor which the inverter end is connected to (the one that runs back to the main db).
so by doing this, should there be overload or earth fault on that circuit, thevRCBO will trip and disconnect the line at the board end and open the contactor disconnecting both line and neutral from the inverter. But would this disconnect or open the contactor in the right time to comply?
Just a thought?? No idea if it would be ok or not
Two RCDs may not suffice, if the inverter is earth referenced through a solid link then it should work, but if it's earth referenced through a resistance or through fortuitous connection it may not.
The bottom line that most of us were getting at is that the circuit should be designed so that RCD protection is not required, which isn't exactly difficult really.
Hi
Im lost, whats this disconnect both ends about? The inverter must disconect within 5 secs, as we cant connect to Final circuit the a Distribution circuit it is, 5 Sec disconection.
Cheers
It it will hold it closed sorry, then when triggered it will release the contactor and shut the PV end off.
Even if it's on an MCB you will still have the issue of two supplies.
Hi
Im lost, whats this disconnect both ends about? The inverter must disconect within 5 secs, as we cant connect to Final circuit the a Distribution circuit it is, 5 Sec disconection.
Cheers
Don't see why an RCD would be affected by the inverter being referenced to earth?Two RCDs may not suffice, if the inverter is earth referenced through a solid link then it should work, but if it's earth referenced through a resistance or through fortuitous connection it may not.
The bottom line that most of us were getting at is that the circuit should be designed so that RCD protection is not required, which isn't exactly difficult really.
As far as I am aware, these particular inverters do not require type B RCDs.
I know that the earth and neutral are linked by visual inspection.
I was interested in why there is a neutral for 3 phase inverters, when to my mind there would be no need, as there is no transformer to connect a neutral to the star point.
As no one I asked could provide an answer as to whether a neutral is required, I thought I would investigate the next inverter I got hold of.
There is a wiring block to connect the output conductors, then some short lengths of conductors to over voltage surge arresters, with blank modules for the earth and neutral, the other side of the surge arresters, is where the earth and neutral are linked, with only the earth and phase conductors continuing into the innards of the inverter.
Something that puzzles me, is how the inverter knows there is a connection to the grid?
Does the inverter pause the output from the inverter to measure the grid, or is there some manner that the inverter can differentiate between the grid voltage and the inverter voltage?
It came up as a result of the mention of a PV circuit being provided with RCD protection.
I suggested the only way a PV circuit which requires 30mA RCD could be provided with it is if the RCD disconnects both ends of the supply.
But I thought it would illustrate why a PV circuit should be designed to not need RCD protection,
I didn't mean a shunt, I mean one of those things you use to fix an indicator to an MCB for example, I can't think what they are called, I call them a shunt, it's probably not but Hager do them anyway.
Hi
Only one rcd would be required at teh output of the Inverter.
Cheers
Don't see why an RCD would be affected by the inverter being referenced to earth?
Difficult, I'd say virtually impossible with a TT installation.