Just a quick one....
When working out cable calcs I have always used the Ib<equal to In<equal to Iz.
Unless overload protection is not required for the cable Iz can be taken from Ib.
(It)...i believe is the tabulated values in the tables in appendix 4.
Iz is the current-carrying capacity of the cable after other factors have been taken into account such as grouping, ambient temperature, thermal insuation and protective device etc
Then go to the appendix 4 tables relating to the cable in question and pick the size cable which has a higher value than your Iz value.
A friend of mine is doing a home study and its shown as an example where It is calculated from In over the factors, then Iz is taken from the tables. I could be missing the point somewhere, but I'm sure it's wrong.
Any replies would be appreciated.
Paul
When working out cable calcs I have always used the Ib<equal to In<equal to Iz.
Unless overload protection is not required for the cable Iz can be taken from Ib.
(It)...i believe is the tabulated values in the tables in appendix 4.
Iz is the current-carrying capacity of the cable after other factors have been taken into account such as grouping, ambient temperature, thermal insuation and protective device etc
Then go to the appendix 4 tables relating to the cable in question and pick the size cable which has a higher value than your Iz value.
A friend of mine is doing a home study and its shown as an example where It is calculated from In over the factors, then Iz is taken from the tables. I could be missing the point somewhere, but I'm sure it's wrong.
Any replies would be appreciated.
Paul