Query on cable calcs | on ElectriciansForums

Discuss Query on cable calcs in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 30, 2008
Messages
86
Reaction score
4
Just a quick one....
When working out cable calcs I have always used the Ib<equal to In<equal to Iz.
Unless overload protection is not required for the cable Iz can be taken from Ib.
(It)...i believe is the tabulated values in the tables in appendix 4.
Iz is the current-carrying capacity of the cable after other factors have been taken into account such as grouping, ambient temperature, thermal insuation and protective device etc
Then go to the appendix 4 tables relating to the cable in question and pick the size cable which has a higher value than your Iz value.

A friend of mine is doing a home study and its shown as an example where It is calculated from In over the factors, then Iz is taken from the tables. I could be missing the point somewhere, but I'm sure it's wrong.

Any replies would be appreciated.
Paul
 
Last edited:
It is the tabulated ccc of a cable
Iz is the in service ccc of a cable.
;-)
That's what I thought but in my friends home study it's the other way round... (It) is the worked out value from In over factors rather than (Iz)worked out from In over factors. Then Iz was the value taken from the tables to get the cable size.
 
Last edited:
all your doing is substituting the Iz prefix for It , its a minor detail that has no effect on the outcome of the equation if carried out in the right steps.
to be honest , i do it the same way as your mate and use It , the end figure stays the same though so makes no odds.
 
all your doing is substituting the Iz prefix for It , its a minor detail that has no effect on the outcome of the equation if carried out in the right steps.
to be honest , i do it the same way as your mate and use It , the end figure stays the same though so makes no odds.
Your right it's only minor detail...
(It) was the worked out value and (Iz) was the value taken from the tables in appendix 4 to get the cable size, which I thought was the other way around.
Cheers anyway Biff :)
 

Reply to Query on cable calcs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top