If there is such a thing as a 400V LED driver, then yes. There's no need for a neutral and no need for loads to be balanced. Just connect them between any two lines and that's that. I'm not familiar with units that take 400V AC input though. And, uh, why?
 
the singlephase load requires 240V. the only way to get that from a 3 phase 415V supply is Ph -N, N being the star point.
Agreed but the star point requires no connection to neutral. I regularly used to demonstrate this by having three 60w lamps connected across three phases and the neutrals floating and just connected together.
 
I think this hole thread is a fishing exercise from previous posts. It is not uncommon in large commercial or industrial installations to have three phase lighting circuits which incorporate a single neutral conductor provided you have a linked triple pole protective device.
 
Enlighten me fellas, how does it work without a neutral? i thought a neutral was required to create a potential difference thus allow the current to flow. Be gentle...
 
Enlighten me fellas, how does it work without a neutral?. Be gentle...
The whole basis of the three opposing phases is they always add to zero , making their own neutral when stared , saving on 3x Line currents flowing up return !

Hence the preoccupation with balanced loads so neutral , doesnt get cooked up.
 
Thanks for the replies, although I'm not sure why people are saying that this thread is an attempt at a 'wind up' or 'Fishing'- I am simply asking a question in good faith, as an electrician who has worked overwhelmingly in domestic installations and is trying to progress to commercial and industrial installations as well as design. Anyway, I realise that 400V, 3 Phase LED lighting is probably overkill in this case. Single Phase would indeed do the job well, if it wasn't for the length of the cable run, which would be about 50m from the Consumer Unit to the last light fitting, which may entail unacceptable voltage drop, and in turn require the use of 2.5 or 4mm conductors, which could be rather difficult to terminate in lighting accessories. As for the existence of 400V LED Drivers, they do exist (Although someone made a good point about them likely requiring neutral connection)- try Google if you don't believe me! Your responses have made me rethink the 400V three phase option- especially the fact that a malfunction of one or more of the lights could unbalance the loading of the circuit.
 
'As for the existence of 400V LED Drivers, they do exist (Although someone made a good point about them likely requiring neutral connection)- try Google if you don't believe me! '

Out of curiosity I did a google search and found this example:

LPFH-60-54 - MEAN WELL - TRC Electronics - http://www.trcelectronics.com/View/Mean-Well/LPFH-60-54.shtml

I note though that the input voltage specification is 200 - 400V ac to 'Meet 277Vac and 347Vac input requirements of North America'. At first glance then, the manufacturer has in mind two operating voltages lower than the upper figure of 400V. The three phase supply in my road in London is 242 x square root of 3 = 420V.
 
As was stated earlier, if you are planning to switch them all on at the same time, beware of the inrush current, as this may cause nuisance tripping of the protective device. I recently looked at some 140w led fittings .. inrush current was 10.2A per fitting!
 

Reply to Question regarding 400V three phase lighting connected in Delta, without Neutral. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N
A
So you have a total of 550w @ 230v, you shouldn't be challenging a B6 on overload but clamping it can confirm this. Do you have an earth leakage...
Replies
4
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top