I regularly used to demonstrate this by having three 60w lamps connected across three phases
This works in star with a floating star point using filament lamps, because the loads, despite their large temperature coefficient, are approximately resistive for a small change in temperature, and at least are always electrically continuous. Electronic drivers are switched-mode power supplies that work at approximately constant power input so they can have negative dynamic resistance, i.e. the current falls as the voltage rises. A unit that, through minor differences in load or construction tolerance, is using slightly less current, will receive slightly higher voltage just as though they were in series on a single pahse supply. This will further reduce the current and the system will experience positive feedback, almost inevitably swinging to extreme unbalance until one unit receives too low a voltage and shuts down. At that time almost the full 400V will be across the unit that is still operating, until it decides not to operate any more! The same will occur if one unit starts up slightly quicker than another.

In summary - identical single-phase loads in star with floating star point, OK with constant resistance loads like heating elements, no good with electronic loads even if apparently perfectly balanced.
 
Agree and it would be foolhardy to install any lighting circuits across a three phase supply with no neutral.
 
Single Phase would indeed do the job well, if it wasn't for the length of the cable run, which would be about 50m from the Consumer Unit to the last light fitting, which may entail unacceptable voltage drop, and in turn require the use of 2.5 or 4mm conductors, which could be rather difficult to terminate in lighting accessories.

So make the main run in 4mm², or whatever, then into a junction box and drop down to 1mm² or 1.5mm² for the final link to the fittings.
 
Single Phase would indeed do the job well, if it wasn't for the length of the cable run, which would be about 50m from the Consumer Unit to the last light fitting, which may entail unacceptable voltage drop, and in turn require the use of 2.5 or 4mm conductors, which could be rather difficult to terminate in lighting accessories.

So make the main run in 4mm², or whatever, then into a junction box and drop down to 1mm² or 1.5mm² for the final link to the fittings.
 
You know @westward10 that sorcery you do with the lights you ought to set up a rig and demonstrate that here on the forum. It would be great to demonstrate graphically to all the theory of circuits and 3 phase etc. Of course you would have to warn us not to do it at home.
 
Anyway, I realise that 400V, 3 Phase LED lighting is probably overkill in this case. Single Phase would indeed do the job well, if it wasn't for the length of the cable run, which would be about 50m from the Consumer Unit to the last light fitting, which may entail unacceptable voltage drop, and in turn require the use of 2.5 or 4mm conductors, which could be rather difficult to terminate in lighting accessories.

It would be an unconventional, and in my opinion design which will lead to maintanence issues in the future as the drivers will be non-standard and hard to replace. You will also be putting 400V where nobody normally expects to find it.
You'll also need the neutral anyway as you almost certainly won't get emergency lighting that'll work on 400V.


2.5mm is pretty common as a minimum size of conductor for lighting circuits in commercial jobs. It's not too bad to terminate into the usual fittings (rock rose etc) if you're careful.

Have you actually calculated the voltage drop or are you just guessing?
Even if you were daft enough to put the whole lot on to one single phase circuit a quick calculation suggests that 1.5mm would be fine if you connected the whole load at the very end of a 60m cable run. So in a real world scenario where the load would be distributed along the length of the circuit, and you'd almost certainly spread them across at least two circuits for a bit of redundancy should one circuit trip, I can't see any issue.
 

Reply to Question regarding 400V three phase lighting connected in Delta, without Neutral. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N
A
So you have a total of 550w @ 230v, you shouldn't be challenging a B6 on overload but clamping it can confirm this. Do you have an earth leakage...
Replies
4
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top