Testing R1/R2 on 10mm/4mm T&E cable and the reading is 0.00? Never had this before, can I record 0 on the cert?
 
Sorry Pete and mdj,on my testers you just select continuity if there is a scale selection I’m not aware of it?...
Fair comment fella, some testers have different scales, and if your on the wrong one a zero showing isn't unusual hence mine and Petes question.
 
Resistance of copper per metre(mohms/M) appendix I of OSG:

10mm=1.83
4mm=4.61

1.83+4.61=6.44

6.44*8=51.52

51.52/1000=0.05 ohms.
 
Sorry Pete and mdj,on my testers you just select continuity if there is a scale selection I’m not aware of it?...
Fair comment fella, some testers have different scales, and if your on the wrong one a zero showing isn't unusaul hence mine and Petes question.
Resistance of copper per metre(mohms/M) appendix I of OSG:

10mm=1.83
4mm=4.61

1.83+4.61=6.44

6.44*8=51.52

51.52/1000=0.05 ohms.
Show off :D
 
Have you got any old or new lengths of cable you can test your MFT with?

Do you also have a ‘Calibration Card or a calibration box’?

We used the Kewtech KT63 MFT in training and they’re
auto-ranging.
 
What you could do it add a known higher resistance in the circuit as your circuit resistance is so low. Take a length of 1.0 singles which will add significant resistance and measure this resistance, then incorporate this into the circuit and remeasure. If you deduct the resistance of the first reading from the second you may get a result for the cable.
 
Resistance of copper per metre(mohms/M) appendix I of OSG:

10mm=1.83
4mm=4.61

1.83+4.61=6.44

6.44*8=51.52

51.52/1000=0.05 ohms.
Thanks strima, that calculation with Archie’s advice would account for the zero reading,
I am going to run some test tests tomorrow to put my mind at ease that the testers are working correctly, I’ll cut cable to exact lengths and then compare to osg/byb
 

Reply to R1+R2 of zero zilch nothing?...... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
541
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top