Probably will trip the RCD if the RCD is in the circuit after the MCB then what you are doing is slapping a few volts and ma's through the RCD even though the voltage you are testing at is low the current used in the R1 and R2 test my exceed that of the RCD its being tested across 2 conductors causing and imbalance thus the RCD trips , as sintra says do a to stage test or tempuaraly remove the RCD oh and what ever you do dont do an IR test with the RCD in the circuit
just read nicks post and he explains it a lot better than i did,
i always disconnect every conductor of the circuit from the board when im doing that test, so ive never had the problem you said, but it makes sense that it could take the rcd out tho.
I have the same problem now on an EICR.
Radial Circuit is wired out an MCB, L+N through a bog standard RCD with the cpc crimped through. I have LN+E Disconnected out of the DB I have shorted my cpc And R1 with R1+R2 leads, go to the last socket and a recently calibrated megger 1502 trips the rcd on th ohms scale when trying to read R1+R2??
Anyone??
By pass the RCD, the RCD is seeing current on the Line but nothing on the neutral so is tripping out.
As it's an EICR it is acceptable to carry out an R2 only.
Reply to R1 + R2 on RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It was >999 on all, tested cables connected and individually, he ce the reason i came on here to ask for ideas
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...