Probably will trip the RCD if the RCD is in the circuit after the MCB then what you are doing is slapping a few volts and ma's through the RCD even though the voltage you are testing at is low the current used in the R1 and R2 test my exceed that of the RCD its being tested across 2 conductors causing and imbalance thus the RCD trips , as sintra says do a to stage test or tempuaraly remove the RCD oh and what ever you do dont do an IR test with the RCD in the circuit
 
what make of RCD ?? do you have a image of the rcd ..

not too sure, it was just on a 2391 test board. i was thinking along the line of nickblake. The 1651b tester is new so dont think its faulty as all readings are the same as other tester
 
just read nicks post and he explains it a lot better than i did,
i always disconnect every conductor of the circuit from the board when im doing that test, so ive never had the problem you said, but it makes sense that it could take the rcd out tho.
 
I have the same problem now on an EICR.
Radial Circuit is wired out an MCB, L+N through a bog standard RCD with the cpc crimped through. I have LN+E Disconnected out of the DB I have shorted my cpc And R1 with R1+R2 leads, go to the last socket and a recently calibrated megger 1502 trips the rcd on th ohms scale when trying to read R1+R2??
Anyone??
 
By pass the RCD, the RCD is seeing current on the Line but nothing on the neutral so is tripping out.

As it's an EICR it is acceptable to carry out an R2 only.
 
Are you sure the circuit is isolated. I would recommend you disconnect the live from the mcb, and connect to the earth bar
 
Link out at board, link out at last fitting, and Carry out the test at the RCD - one lead on line incomer the other on outgoing
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
R1 + R2 on RCD
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
jreid67,
Last reply from
hightower,
Replies
24
Views
8,459

Advert

Back
Top