r1+r2 reading | on ElectriciansForums

Discuss r1+r2 reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

beaver74

on a pme system wre a rod is used to seperate metal parts from pme terminal how would you record r1+r2 of cpc conected to rod and r1+r2 of cpc conected to pme terminal ie swa


got some external lighting in midle of a lawn wired in swa and armer is continious but seperated from fitting metal work so that swa will have a good earth loop reading
earth conductive part of lighting is conected to 3 rods spead around circuit via 3rd core of swa so as to seperate from pme terminal but the circuit will have rcd protection at the main intake so r1+r2 of swa and r1+r2 of lighting circuit on the rod can not be recorded together as they are seperate
 
Dont quite understand what your saying, but the supply authorities seriously frown upon you using a pme system out side the equipotential zone. therefore you should have created a seperate tt system for what ever you are supplying outdoors. You only need verify your Ra and/ or R2.
 
Dont quite understand what your saying, but the supply authorities seriously frown upon you using a pme system out side the equipotential zone. therefore you should have created a seperate tt system for what ever you are supplying outdoors. You only need verify your Ra and/ or R2.
the system will be t.t as 3rd core of swa is seperated from pme and attached to a rod
 

Reply to r1+r2 reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top