So how would you word 'test method 1' when testing for CPC? Without the book in front of me I thought it was worded r1 + r2. Which uses a temp link between live and earth at the board. And testing using a low resistance ohmeter to get a continuity result.
 
this is from a guy on here who knows what he is talking about i suggest you go back to college or do some revision

If you are R1+R2 testing on a radial circuit then you simply isolate all power at the DB i.e main switch off, place a link between Line and Earth of the circuit you want to test, then go to the end of that circuit and measure the continuity between Line and Earth.

For a ring main again isolate, joint Line 1 to Earth 2, Line 2 to Earth one and measure at each socket on that ring circuit, the highest reading you get being recorded as the R1+R2 for that ring circuit.
 
Yeah its all down to capital letters thought it would be straight forward sorry guys as i mentioned it was a lighting circuit so thought you would know yes (R1 + R2) temp link in board or join together in a connector my personal prefrence.
 
osg only uses r1 +r2 and then R1 + R2 on the ring test to stop confussion
all circuits with a line conductor and cpc can and should be tested for the R1 and R2 value ,
 
Last edited by a moderator:
R 1 + R 2 = line and CPC on any cct

r 1 , r 2 , r n = end to end continuity on ring final ccts

its all in 7671/ guidance note 3 or the OSG

when you look at this section on testing does anyone else feel we are underpaid for the amount of knowledge we have
sparks are by far the best trade - HOORAH
 
Dont worry yourselves ive sorted the problem thanks for all the help :) , it appered to be a faulty length of wire, managed to rip it out and put a new piece in without to much damage as i pulled it in the capping it was just getting around the corners.
The cable seemed to have a bulge in it when i pulled it out, so spliced it and the line seemed to have a a little blemish in it which was touching the cpc with no obvious sign of penertration damage, so must of been faulty cable.
 
Not some of that imported junk was it?....quality cable almost never has problems like that....impact damage from a hammer etc can cause the cpc to penetrate a core with no obvious damage to the sheath.
 
Seems like alot of noise over very little.
got to disagree on that one Si, incorrect terminolgy may not seem that important but in my opinion the guys are right, if you start mixing things up then where does the confusion end?

does a main bond become a main earth or an ohm an amp

the replys were not directed at the op asking the question but to the incorrect answers he was given, if he is learning then its best to learn the correct way from the start.
 
Last edited by a moderator:

Reply to r1 + r2 testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
614
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top