i have installed a 4mm radial circuit protected by 32a mcb feeding 5 twin skts, customer now wants 1 more skt but have run out of 4mm cable. If i run last leg in2.5 cable will i be complying with current regs ?
 
Yes you will be.
It will be classed as a spur, so only one double socket can be used unless you use an FCU.
No different really to spurring off of a RFC.
Have a look in Appendix 15 of BS7671 if you want to check.
 
Last edited by a moderator:
reg 433.1 "an unfused spur run in 2.5mm cable should feed one single or one double twin socket - outlet only"
so yes is the answer :)
 
i just thought In had to be equal or greater than ib and It had to be equal In. if you get me

?Yes mate but as has been mentioned its in appendix 15 and as Phil has said there is not a problem as long as its only a single or twin socket outlet , stick an FCU on it and the last leg could be wired in 1.5mm twe
 
I get you. But if the design current will be 26A 2x13. The tabulated value is 28A
Now if the load of either socket goes above 13A then its fuse will blow in the plug, disconnecting the load, so you could argue that the cable is protected by a 26A fuse so (In = Ib) < It.

And its in the regs as mentioned!
 
Last edited:
The circuit protection device doesn't have to be at the beginning of a circuit. It can be at the end, i.e. the fuse(s) in the plug(s).

So the cable cannot be overloaded. That's why only one is allowed without an FCU.

One socket, that is.
 
Last edited by a moderator:

Reply to radial circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Why aren't you asking them?
Replies
5
Views
810
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top