I need to put in 4 sockets in a shop, where the sockets are going is a 6mm radial from an old circuit, its on a 32a rcbo, can i pull this 6mm into a 4 pole isolator and run a ring out of it, iv looked through the regs and cant really find anything thats says i cant.

[ElectriciansForums.net] Radial to Ring
 
Totally Agree, these ring configurations were once very popular with councils, and even a on some of the private housing estates in the 60's...

I dare say there will be many here that haven't seen or come across them, (same as the so-called lollypop ring) and no doubt condemn them because they are not described in BS7671. But the truth is they Both conform with all the requirements of a final ring circuit....
 
Where I used to work I was told to fail this type of cct
Alarently they were incorrectly wired. Which i looked into and didnt agree with,
Also told two different size cables cannot be terminated under the same termination screw....
I couldn't find anything in the regs to support this.
 
Where I used to work I was told to fail this type of cct
Alarently they were incorrectly wired. Which i looked into and didnt agree with,
Also told two different size cables cannot be terminated under the same termination screw....
I couldn't find anything in the regs to support this.

It can't be a failed can it Rich.

If you had 12 sockets say on the ground floor, and you have 12 JBs, each JB had a single cable going out to a socket, theoretically you have a single spur at each point on the ring, which as always been allowed, the only difference from convention is that instead of spurring off a socket your spurring a JB.

I suppose you could argue that your not spurring of a socket, but by spurring off a JB it must surely be safer, instead of double socket plus another double, 4 connection points, you will only ever have 2 points.

Yes the JBs could and likely were inaccessible, but the regs is never been retroactive and though I doubt you would wire a circuit like this now, in industrial situations I've seen and would still wire large rings like this, using tap off points.

As you say mate no reg against 2 different size conductors in one terminal as long as you conform to regs 526 and 526.1 in particular. Besides these rings were normally done in 2.5 or 7/029 and the spur the same size.
 
I cant remember the reg now but im sure it says something along the lines of an unfused spur for every s/o. I will check later but if thats the case you have now have no s/o on the ring main.
 
A lot of council and miners mansion housing back in the 60's was wired similar to this.

You would have a ring running around, and at every socket point the ring would go into a JB and then a single cable out to the socket, it was felt you used less cable which I suppose you did, easier chasing in a single cable rather than 2 cables and easier connecting into a socket.

Always threw me at first, but got use to it

Ironic really saved cable but used more jb,s seen it a lot on old pit houses near me,last time I saw it was a few years ago when I went to do work on my mates house which he had bought a few years earlier,and had allegedly been rewired before he bought it turned out owner had just replaced socket fronts and leg to jb,leaving old rubber ring going back to cu boy was my mate peed off.
 

Reply to Radial to Ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
762
  • Question
Why aren't you asking them?
Replies
5
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top